Interference-free bus terminals

Interference-free bus terminals 1:

Implementing interference-free bus or EtherCAT Terminals in safety applications

When a bus terminal or EtherCAT Terminal is described as interference-free, this means that the downstream terminal will be passive in a safety application (e.g., during all-pole disconnection of a potential group).
In this context, the terminals do not constitute an active part of the safety controller and do not influence the safety integrity level (SIL) or performance level (PL) achieved in the safety application.
Please refer to the TwinSAFE Application Manual, chapter “All-pole disconnection of a potential group with downstream interference-free standard terminals (Category 4, PL e)” and subsequent sections.

 

Notice

Note the hardware version

Please refer to the “Technical data” and “Firmware compatibility” sections for information on the hardware version and interference-free nature of the respective bus terminal!
Only terminals with the correct hardware version may be used – otherwise the achieved SIL/PL may be affected!

The terminals regarded as interference-free at the point that this document was drafted are listed in the following tables along with their respective hardware versions.

Bus terminals

Terminal name

From hardware version

KL2134

09

KL2408

05

KL2424

05

KL2432

00

KL2434

00

KL2809

02

KL9110

07

ED Terminals

Terminal name

From hardware version

ED1859

00

ED2008

00

ED2032

00

ED2034

00

ED2807

00

ED2808

00

ED2809

00

ED2828

00

ED2838

00

ED2887

00

ED2889

00

ED9100

00

ED9110

00

ED9183

00

ED9184

00

ED9186

00

ED9188

00

ED9189

00

ED9410

00

EL Terminals

Terminal name

From hardware version

EL2004

15

EL2008

07

EL2014

00

EL2022

09

EL2024

06

EL2034

06

EL2042

06

EL2044

01

EL2068

00

EL2212

00

EL2258

00

EL2407

00

EL2409

00

EL2489

00

EL2809

01

EL2819

00

EL2828

00

EL2838

00

EL2869

00

EL2872

01

EL2878-0005

00

EL9110

13

EL9184

00

EL9185

00

EL9186

00

EL9187

00

EL9188

00

EL9189

00

EL9410

16

ELX Terminals

Terminal name

From hardware version

ELX1052

00

ELX1054

00

ELX1058

00

ELX2002

00

ELX2008

00

ELX2792

00

ELX3152

00

ELX3158

00

ELX3181

00

ELX3184

00

ELX3202

00

ELX3204

00

ELX3252

00

ELX3312

00

ELX3314

00

ELX3351

00

ELX4154

01

ELX4181

00

ELX5151

00

ELX6233

00

ELX9560

03

External wiring

The following requirements are to be ensured by the system manufacturer and must be incorporated into the user documentation.

Summary of safety levels

Feedback prevention measures

DIN EN ISO 13849-1

IEC 61508

EN 62061

Cable short-circuit fault exclusion

 

max.

Cat. 4

PL e

max. SIL3

max. SIL2*

Ground return and all-pole disconnection

max. SIL3

WARNING

Please follow the instructions for operating interference-free terminals!

  • All terminals in a potential group must be interference-free!
  • Make sure that, even in the event of a fault, no power can be fed back through external wiring!