Watchdog behavior in case of a bus error | Index 0x80n:05 “Watchdog”
The setting in index 0x80n0:05 “Watchdog” defines how the output should assume a safe state in the event of a bus error. The following table shows the available settings.
Watchdog behavior in case of a bus error | Index 0x80n:05 “Watchdog” 1:Fig.28: PWM watchdog settings
Desired state
of the output in the event of a bus error
Specification in 0x80n0:05 “Watchdog”
(n = 0 for PWM1, n = 2 for PWM2, n = 4 for PWM3, n = 6 for PWM4)
set to specified value
0: Default watchdog value
  • The specified pulse width “PWM Output"” of the output is set to the value defined in index 0x80n0:13 “Default Output”.
  • The period specified for the “PWM Period” process data value is set to the value defined in index 0x80n0:17 “Default Period”.
set to specified value via ramp
1: Watchdog ramp
  • The specified pulse width “PWM Output” of the output is switched to the value specified in index 0x80n0:13 “Default Output Ramp”
    via the ramp defined in index 0x80n0:14 “Default Output” (linear change [digit/ms]).
Retain current value
2: Last value
The output retains the current state.
Switch to high-resistance
(Tristate)
3: “High impedance”
The output is switched to high-impedance.
Notice
Apply watchdog settings for power supply units that can be configured via EtherCAT
  • If a power supply unit that can be configured via EtherCAT is used for the external power supply – for example, an EL9501 power supply terminal (0…20 V DC, 0…2 A) – the settings on this power supply unit must also be configured according to the requirements.
  • If no external power is supplied in the event of a bus error, no output voltage is generated.
Ramp
You can define the time to reach the default value when the watchdog behavior is set to the value 1 "Watchdog ramp".
Watchdog behavior in case of a bus error | Index 0x80n:05 “Watchdog” 2:
t: time in ms until the default value is reached.
ncurrent : the last output value that was received by the controller before the communication interruption.
ndefault : default value (CoE parameter 0x80n0:13).
vramp : ramp velocity in digits/ms (CoE parameter 0x80n0:14).
Tristate
In the event of a bus error, the output can be switched to a tristate state, actively to 24 V and high-impedance. The high-resistance tristate state ensures that the respective output behaves as if it were not connected. This means that the outputs of other outputs/devices connected to this output are not affected. The associated output takes on the same output voltage as the other active devices.
Diagnostics in case of bus error
The triggering of the watchdog event is indicated by:
LED 1: “Run”, LED 2: “Dev error”
Process data
DiagMessages “
” when communication
is resumed
“Run” blinks, “Dev error” lights up red
Watchdog behavior in case of a bus error | Index 0x80n:05 “Watchdog” 3:
Text ID: 0x8114 Output Cycle Counter watchdog has triggered
Text ID: 0x8105 PD watchdog has triggered