Interference-free bus terminals
Interference-free bus terminals 1:
Implementing interference-free bus or EtherCAT Terminals in safety applications
When a bus terminal or EtherCAT Terminal is described as interference-free, this means that the downstream terminal will be passive in a safety application (e.g., during all-pole disconnection of a potential group).
In this context, the terminals do not constitute an active part of the safety controller and do not influence the safety integrity level (SIL) or performance level (PL) achieved in the safety application.
Please refer to the TwinSAFE Application Manual, chapter “All-pole disconnection of a potential group with downstream interference-free standard terminals (Category 4, PL e)” and subsequent sections.
Notice
Note the hardware version
Please refer to the “Technical data” and “Firmware compatibility” sections for information on the hardware version and interference-free nature of the respective bus terminal!
Only terminals with the correct hardware version may be used – otherwise the achieved SIL/PL may be affected!
The terminals regarded as interference-free at the point that this document was drafted are listed in the following tables along with their respective hardware versions.
Bus terminals
Terminal name
From hardware version
KL2408
05
KL2809
02
KL2134
09
KL2424
05
KL9110
07
ED Terminals
Terminal name
ED2008
00
ED2032
00
ED2034
00
ED2807
00
ED2809
00
ED2828
00
ED2838
00
ED2887
00
ED2889
00
ED9100
00
ED9110
00
ED9184
00
ED9410
00
EL Terminals
Terminal name
EL2004
15
EL2008
07
EL2014
00
EL2022
09
EL2024
06
EL2034
06
EL2042
06
EL2044
01
EL2068
00
EL2212
00
EL2258
00
EL2407
00
EL2409
00
EL2489
00
EL2809
01
EL2819
00
EL2828
00
EL2838
00
EL2869
00
EL2872
01
EL2878-0005
00
EL9110
13
EL9184
00
EL9185
00
EL9186
00
EL9187
00
EL9410
16
ELX Terminals
Terminal name
ELX1052
00
ELX1054
00
ELX1058
00
ELX2002
00
ELX2008
00
ELX2792
00
ELX3152
00
ELX3158
00
ELX3181
00
ELX3184
00
ELX3202
00
ELX3204
00
ELX3252
00
ELX3312
00
ELX3314
00
ELX3351
00
ELX4154
01
ELX4181
00
ELX5151
00
ELX6233
00
ELX9560
03
External wiring
The following requirements are to be ensured by the system manufacturer and must be incorporated into the user documentation.
Summary of safety levels
Feedback prevention measures
DIN EN ISO 13849-1
IEC 61508
EN 62061
Cable short-circuit fault exclusion
max.
Cat. 4
PL e
max. SIL3
max. SIL2*
Ground return and all-pole disconnection
max. SIL3
WARNING
Please follow the instructions for operating interference-free terminals!
  • All terminals in a potential group must be interference-free!
  • Make sure that, even in the event of a fault, no power can be fed back through external wiring!