Interference-free bus terminals
Interference-free bus terminals 1:
Implementing interference-free bus or EtherCAT Terminals in safety applications
When a bus terminal or EtherCAT Terminal is described as interference-free, this means that the downstream terminal will be passive in a safety application (e.g., during all-pole disconnection of a potential group).
In this context, the terminals do not constitute an active part of the safety controller and do not influence the safety integrity level (SIL) or performance level (PL) achieved in the safety application.
Please refer to the TwinSAFE Application Manual, chapter “All-pole disconnection of a potential group with downstream interference-free standard terminals (Category 4, PL e)” and subsequent sections.
Notice
Note the hardware version
Please refer to the “Technical data” and “Firmware compatibility” sections for information on the hardware version and interference-free nature of the respective bus terminal!
Only terminals with the correct hardware version may be used – otherwise the achieved SIL/PL may be affected!
The terminals regarded as interference-free at the point that this document was drafted are listed in the following tables along with their respective hardware versions.
ED Terminals
Terminal name
From hardware version
ED1859
00
ED2008
00
ED2032
00
ED2034
00
ED2807
00
ED2808
00
ED2809
00
ED2828
00
ED2838
00
ED2887
00
ED2889
00
ED9100
00
ED9110
00
ED9183
00
ED9184
00
ED9186
00
ED9188
00
ED9189
00
ED9410
00
External wiring
The following requirements are to be ensured by the system manufacturer and must be incorporated into the user documentation.
Summary of safety levels
Feedback prevention measures
DIN EN ISO 13849-1
IEC 61508
EN 62061
Cable short-circuit fault exclusion
max.
Cat. 4
PL e
max. SIL3
max. SIL2*
Ground return and all-pole disconnection
max. SIL3
WARNING
Please follow the instructions for operating interference-free terminals!
  • All terminals in a potential group must be interference-free!
  • Make sure that, even in the event of a fault, no power can be fed back through external wiring!