Counter mode
The CX7050 Embedded PC can be configured as an up/down counter that enables the counting of a pulse. The embedded PC is suitable for fast counting tasks with a cut-off frequency of up to 100 kHz, whereby the CX7050 can be operated in 1-counter mode.
Counter mode 1:
Configurable inputs and outputs in counter mode.
The CX7050 supports three operation modes in counter mode:
In addition, output 1 can be switched depending on the counter value. Output 2 can be switched from the PLC. This allows fast control signals for field devices to be used and switched.
The operation modes are set in TwinCAT via CoE objects.
Up/down counter
In the up/down counter operation mode, the pulse to be counted is detected by digital input 1. The counting direction is specified by digital input 2.
If there is a high level at input 1 and at the same time at input 2, the counter counts upwards. If there is a high level at input 1 and a low level at input 2, the counter counts downwards.
Up counter
In this operation mode, the signal is detected at digital input 1.
Down counter
Counter mode 2:
Technical data, multi-function I/Os in counter mode.
Technical data
CX7050
Number of counters
1 x up/down counter, 1 x up or down counter
Nominal voltage
24 V DC (-15 %/+20 %)
Specification
EN 61131-2, type 3
Signal voltage "0"
-3…+5 V
Signal voltage "1"
11…30 V
Cut-off frequency
Up/down counter: 20 kHz1), counting in one direction only: 100 kHz
Counter depth
32-bit
Max. output current
24 V/0.5 A (short-circuit proof)
Special features
Set counter, switch outputs, reset counter
Connection cross-section
e*: 0.08…1.5 mm²,
f*: 0.25…1.5 mm²,
a*: 0.14…0.75 mm²
Connection cross section AWG
e*: AWG 28…16,
f*: AWG 22…16,
a*: AWG 26…19
Strip length
8 … 9 mm
1) The up/down counter can also count up to 100 kHz, only with a direction reversal the counting frequency must be <= 20 kHz, otherwise pulses will be lost.
*e: single-wire, solid wire; f: stranded wire; a: with ferrule
