Forwarding parameter and configuration data to the PLC
To be able to transfer the parameter and configuration data to the PLC, these must be sent to the ADS server in the slave. The corresponding option is activated via TwinCAT.
Proceed as follows:
- 1. Select the PROFIBUS slave in the structure tree on the left,
- 2. Activate the SetPrm/ChkCfg handled by ADS Server... option.
- 3. Use port 851 for the first PLC task.
- The data is now sent to the PLC via ADS indication. The data must be accepted and acknowledged in the PLC.
Accepting and acknowledging data in the PLC
First of all, you should check where the data comes from. The CX7031 supports up to 4 slaves, which are coded in the port number of the slave, namely the PROFIBUS address + 0x1000hex.
The telegram is coded in IdxOffset:
- Parameter data: 16#03230020
- Configuration data: 16#03230021
When starting the master, you will always receive two indications, both of which you must acknowledge with Result=0, otherwise an error will be sent to the corresponding PROFIBUS master and the connection will not be established.
Code sample:
i : INT;
sNetId : STRING;
nPort : UINT;
udInvokeId : UDINT;
iCase : INT;
udGroup : UDINT;
udOffset : UDINT;
udLenght : UDINT
ptrByte : POINTER TO BYTE; (* Datenpointer *)
strPrmData2 : ARRAY[0..127] OF BYTE;
strCfgData2 : ARRAY[0..127] OF BYTE;
strPrmData3 : ARRAY[0..127] OF BYTE;
strCfgData3 : ARRAY[0..127] OF BYTE;
fbAdsWriteInd : ADSWRITEIND;
fbAdsWriteRes : ADSWRITERES;
bExecute : BOOL;
stAdsInfo AT %I*: ST_AmsAddr;
nState AT %I*: WORD;
UnKonwnoffset : UDINT;
fbAdsWriteInd(
CLEAR := ,
VALID => ,
NETID => ,
PORT => ,
INVOKEID => ,
IDXGRP => ,
IDXOFFS => ,
LENGTH => ,
DATAADDR => );
IF fbAdsWriteInd.VALID THEN
(* You have to check the NETID and port number if you use ADS notification also for other things *)
i := i + 1;
sNetId := fbAdsWriteInd.NETID; // AMD Net ID from device (CX7031)
nPort := fbAdsWriteInd.PORT; // PB Adresse + 1000 dec
udInvokeId := fbAdsWriteInd.INVOKEID; // for the Response
udGroup := UDINT_TO_DWORD(fbAdsWriteInd.IDXGRP);
udOffset := fbAdsWriteInd.IDXOFFS; // Prm or Cfg Data
udLength := fbAdsWriteInd.LENGTH; // Len of the data
ptrByte := fbAdsWriteInd.DATAADDR; // Pointer from the data
fbAdsWriteRes.RESULT := 0; // Result without Error, if you want to send an Error use "1"
IF nPort = 1002 THEN // Slave with Adress 2
CASE udOffset OF
16#03230020: // Prm Data
MEMCPY(ADR(strPrmData2), ptrByte, udLength);
16#03230021: // Cfg Data
MEMCPY(ADR(strCfgData2), ptrByte, udLength);
ELSE
fbAdsWriteRes.RESULT := 1;
UnKnownOffset := udOffset;
END_CASE
END_IF
IF nPort = 1003 THEN // Slave with Adress 3
CASE udOffset OF
MEMCPY(ADR(strPrmData3), ptrByte, udLength);
MEMCPY(ADR(strCfgData3), ptrByte, udLength);
ELSE
END_CASE
END_IF
IF iCase = 0 THEN
iCase := 10; // Send response
END_IF
END_IF
CASE iCase OF
0: (* WAIT *);
10: (* send ADS-Response *)
fbAdsWriteRes(
NETID := sNetId,
PORT := nPort,
INVOKEID := udInvokeId,
RESULT := ,
RESPOND := TRUE);
fbAdsWriteInd(CLEAR := TRUE); (* confirm ADS-Indication *)
iCase := 20;
20:
fbAdsWriteRes(RESPOND := FALSE);
fbAdsWriteInd(CLEAR := FALSE);
iCase := 0;
END_CASE