LEDs of the power supply in K-bus mode
After switching on, the power supply immediately checks the connected Bus Terminal configuration. Error-free start-up is signalled by the red "I/O ERR” LED being extinguished. If the “I/O ERR” LED blinks, an error in the area of the terminals is indicated. The error code can be determined from the frequency and number of blinks. This permits rapid rectification of the error.
Display | LED | Meaning |
| Us 24 V | Power supply for the CPU module. The LED lights green if the power supply is correct. |
Up 24V | Power supply for terminal bus. The LED lights green if the power supply is correct. | |
K-BUS RUN | K-bus diagnostics. The green LED lights up in order to indicate fault-free operation. "Fault-free" means that the communication with the fieldbus system is also running. | |
K-BUS ERR | K-bus diagnostics. The red LED flashes to indicate an error. The red LED blinks with two different frequencies. |
The I/O error LED blink code
Fast blinking | Start of the error code |
First slow sequence | Error code |
Second slow sequence | Error code argument |
LEDs for K-bus diagnostics
Error code | Error code argument | Description | Remedy |
Persistent, continuous flashing |
| EMC problems |
3 pulses | 0 | K-bus command error |
4 pulses | 0 | K-Bus data error, break behind the power supply | Check whether the Bus End Terminal 9010 is connected. |
n | Break behind Bus Terminal n | Check whether the Bus Terminal n+1 is correctly connected; replace if necessary. | |
5 pulses | n | K-bus error in register communication with Bus Terminal n | Exchange the Bus Terminal on position n. |
6 pulses | 0 | Error at initialization | Exchange Embedded-PC. |
1 | Internal data error | Perform a hardware reset on the Embedded-PC (switch off and on again). | |
8 | Internal data error | Perform a hardware reset on the Embedded-PC (switch off and on again). | |
7 pulses | 0 | Process data lengths of the set and actual configurations do not correspond | Check configuration and terminals for consistency. |
Error code argument
The number of pulses indicates the position of the last Bus Terminal before the fault. Passive Bus Terminals, such as a power feed terminal, are not included in the count.
In the case of some errors, rectification does not cause the power supply to leave the blink sequence. The power supply can only be restarted by switching its supply voltage off and on again.
The CX unit recognizes these terminals automatically on scanning, reads out the terminal types and automatically places them in the System Manager.
K-bus state
The K-bus status is saved in the state byte (see fig. K-bus interface “1”). If the value is 0 the K-bus is operating synchronously and without errors. If the value is <> ”0” there may be a fault, or it may only be an indication that the K-bus cycle is longer than the task, in which case it would no longer by synchronous with the task. The task time should be faster than 100 ms. We recommend a task time of less than 50 ms. The K-bus update time typically lies between one and five ms.
Bit 0 = K-Bus error
Bit 1 = terminal configuration has changed since the start
Bit 2 = process image lengths do not match
Bit 8 = no valid inputs (yet)
Bit 9 = K-bus input update not yet complete
Bit 10 = K-bus output update not yet complete
Bit 11 = watchdog
Bit 15 = acyclic K-bus function active (e.g. K-bus reset)
If there is a K-bus error, this can be reset via the IOF_DeviceReset function block (in the TcIoFunctions.lib).