Slave-Diagnose
DP-State
Each DP slave has a status variable that indicates the current state of that DP slave. This status is maintained in real time, so that it is always adapted to the current DP slave data, and can be linked to a PLC variable (-> DpState of the slave):
Slave-Diagnose 1:
Diagnostic data
Any DP slave can acyclically report DP diagnostic data during data exchange operation. The slave here sets the Diag_Flag in the response to the cyclic Data_Exchange telegram, as a result of which the DP master automatically reads the DP diagnostic data from the slave. This does not affect the Data-Exchange cycle in the Beckhoff DP master, because the DP diagnostic telegram is sent at the end of the cyclic Data-Exchange cycle, and before the beginning of the next cycle. If the DP diagnostic data read from the slave has changed from its previous state, the DP master sets the ExtDiagFlag variable, which can be linked to a variable in the controller program.
The DP slave's current diagnostic data is displayed in the system manager on the slave's Diag tab. It can also be read by the controller program via ADS, which will cause the "ExtDiagFlag" flag to be reset once more:
ADS-Read parameters
Meaning
Net-ID
Net-ID of the master (see the device's ADS tab)
Port
200
IndexGroup
0x00yyF181 (yy = station address of the slave)
IndexOffset
Offset within the diagnosis data
Length
Length of the diagnostic data that is to be read
Data
Diagnostic data
The diagnostic data contains the slave statistics (32 bytes) and the DP diagnostic data sent by the slave (up to 244 bytes), and is constructed as follows:
Offset
Meaning
Slave statistics
0
Receive Error Counter (WORD): The number of faulty telegrams occurring while communicating with this slave.
2
Repeat counter[8] (WORD): The repeat counters indicate how many repeats have had to be made, and how often. Repeat Counter[0] indicates how often it has been necessary to repeat a telegram for this slave once, Repeat Counter[1] shows how often a telegram for this slave has had to be repeated twice, and so on. The maximum number of retries is set with the parameter Max Retry Limit (see Bus parameters dialog). The value range is from 0 to 8, therefore there are 8 repeat counters (for 1 to 8 retries)
18
reserved for extensions
20
NoAnswer Counter (DWORD): The number of telegrams in communication with this slave that have not received an answer. The first time that a slave fails to answer, the telegram is repeated up to MaxRetryLimit times, but if it does not answer even then, further telegrams are not repeated.
24-27
Last-DPV1-Error[4] (BYTE): The most recent faulty DPV1 response is entered here (byte 0: DPV1 service (bit 7 is set, thus indicating an error), byte 1: Error_Decode, byte 2: Error_Code_1 (Error_Class/Error_Code), byte 3: Error_Code_2), see description of the DPV1 error codes
27-31
from 32
DP diagnostic data
There follows a description of the DP diagnostic data
Offset
Meaning
0x00.0
StationNonExistent: slave did not reply to the last telegram
0x00.1
StationNotReady: slave still processing the Set_Prm / Chk_Cfg telegram
0x00.2
CfgFault: slave signaling a configuration error
0x00.3
ExtDiag: extended DiagData available and valid
0x00.4
NotSupported: slave does not support a feature requested via Set_Prm or Global_Control
0x00.5
InvalidSlaveResponse: slave response not DP-compatible
0x00.6
PrmFault: slave reports a paramétrisation error
0x00.7
MasterLock: slave currently exchanging data with another master
0x01.0
PrmReq: re-parameterize and reconfigure slave
0x01.1
StatDiag: slave signaling static diagnosis / DPV1 slave application not yet ready for data exchange
0x01.2
PROFIBUS DP slave
0x01.3
WdOn: DP watchdog on
0x01.4
FreezeMode: DP slave in freeze mode
0x01.5
SyncMode: DP slave in sync mode
0x01.6
reserved
0x01.7
Deactivated: DP slave has been deactivated
0x02.0
reserved
0x02.1
reserved
0x02.2
reserved
0x02.3
reserved
0x02.4
reserved
0x02.5
reserved
0x02.6
reserved
0x02.7
ExtDiagOverflow: too much extended data present
0x03
MasterAdd: station address of master with which slave is exchanging data
0x04,0x05
IdentNumber
ab 0x06
Extended DiagData
Extended DiagData
A distinction is made in the Extended DiagData between identification diagnosis, channel diagnosis and manufacturer-specific diagnosis. The first byte indicates the type of the diagnosis and the length of the associated data. Several diagnostic types can also follow one another in the Extended DiagData.
Header-Byte
Bit
Meaning
0-5
Length of the associated diagnostic data, including header byte
6-7
0 = manufacturer-specific diagnosis (DPV1 is not supported) or DPV1 diagnosis (DPV1 is supported (DPV1_Enable = 1) in associated GSD file)
Module diagnosis
Channel diagnosis
Revision number
Manufacturer-specific diagnosis
The structure of the manufacturer-specific diagnosis may be found in the documentation for the DP slave.