Device configuration dialog

Dialog with device-specific settings.

Device configuration dialog 1:

Setting/command

Area

Default value

Description

Battery type

0..99

1

Only specific for the Beckhoff P24Vxxxx UPS from firmware version >= 24.1.I and required, for example, in order to calculate the remaining battery capacity in battery mode.

Nominal battery capacity

0..99900 [mAh]

3400

Only specific for the Beckhoff P24Vxxxx UPS from firmware version >= 24.1.I and required, for example, in order to calculate the remaining battery capacity in battery mode.

Battery internal resistance

0 - 999 [mOhm]

120

Only specific for the Beckhoff P24Vxxxx UPS from firmware version >= 24.1.I and required, for example, in order to calculate the remaining battery capacity in battery mode.

Battery change interval service

0 - 480 [months]

60 (5 years) and checkbox not checked

Only for the Beckhoff P24Vxxxx UPS from UPS software v3.0.0.8 or higher. An interval service can be configured for this on whose expiry battery change warnings are written into the Windows event log. Use the checkbox to activate or deactivate the function. The number of months before the first warning must additionally be configured in the Edit field. The function is only available if the date of the last battery change and the Windows system time (in the taskbar) have also been correctly set/configured. The UPS service compares the date of the last battery change + interval service with the system date. If the system date is exceeded, a warning is written into the event log. The warning does not provide any information about the actual battery state and can only be used as a reminder to check the battery state/age.

Last service: 01.01.11*

-

-

Displays the date of the last battery change (last service was on January 1, 2011).

Next service: 01.01.16*

-

-

Shows the prospective date of the next battery change (next service is due on January 1, 2016).

Reset interval service message…

-

-

Only for the Beckhoff P24Vxxxx and some APC devices. Updates the date of the last battery change and resets the interval service message. The date is stored in the UPS's EEPROM, and can be examined in the UPS information dialog.

set to: 25.05.12*

-

-

Displays the date which is suggested when resetting the service message. The last battery change/service is updated to this date (the current date is May 25, 2012).

Firmware update...

-

-

Only for the Beckhoff P24Vxxxx from firmware version: >= 21.1.I. Starts a firmware update. Only starts a firmware update if you actually have a suitable new firmware file.

Self-test

-

-

Only for the Beckhoff P24Vxxxx and some APC devices. Executes a self-test and displays the result:

  • "OK" - Test successful, the battery is OK;
  • "BT" failed due to insufficient battery capacity or no battery is present\connected at all;
  • "NG" - Failed as a result of overload;
  • "NA" - Test function does not exist;

Factory settings

-

-

Available from UPS software v3.0.0.8 and higher. Restores the factory settings (default values).

OK

-

-

Saves the settings and closes the dialog. Please do not forget to confirm the settings in the Beckhoff UPS Configuration dialog.

Cancel

-

-

Discards all editable changes.

*) Example values