Fieldbus connection for CANopen CX1500-FB510
ADS Services
Local process image task 1 port 800 or port 801
Data can be read from and written to the local process image. If it is necessary for outputs to be written, it is important to ensure that they are not used by the local PLC, because the local controller will overwrite these values. The data is not associated with a watchdog, and therefore must not be used for outputs that would have to be switched off in the event of a fault.
Index group
Meaning
Index offset (value range)
0xF020
0...2047
0xF030
Outputs
0...2047
0x4020
Flags
0...4095
ADS services
AdsServerAdsState
Data type (read only)
Meaning
String
Start - the local PLC is running
Stop - the local PLC is stopped
AdsServerDeviceState
Meaning
INT
0: Start - the local PLC is running
1: Stop - the local PLC is stopped
AdsServerType
Meaning
String
BX PLC Server
Register port 100
The ADS port number in the Bus Terminal Controller for register communication is fixed, being set at 100.
Index group
Meaning
Hi-Word
Low Word
0 [READ ONLY]
0...127
0...255
Registers in the Bus Coupler
High word, table number of the Bus Coupler
Low word, register number of the table
1...255
0...3
1...255
Register of the Bus Terminal
High word, channel number
Low word, register number of the Bus Terminal
NoteNote when reading the register that the time out for the ADS block is set to a time longer than 1 second.
NoteNote when writing to the registers that the password is set (see the documentation for the particular Bus Terminal).