DP State of the Slaves
Value
No Error - station is exchanging data
1
Station deactivated - slave has been deactivated, temporary state during StartUp
2
Station not exists - slave does not reply on the bus -> check whether slave is switched on, whether PROFIBUS plug is in, correct station address or bus cables
3
Master lock - slave is exchanging data with another master -> remove other master from bus or release slave again by other master
4
Invalid slave response - incorrect answer from slave, occurs temporarily if slave has ceased data exchange as a result of a local event
5
Parameter fault - check whether Bus Coupler / GSD file is correct, that station address is correct or that UserPrmData settings are correct
6
Not supported - DP function is not supported -> check whether GSD file is correct or whether station address is correct
7
Config fault – configuration fault -> check whether the added terminals / modules are correct
8
Station not ready -> station starting up, temporarily displayed during StartUp
9
Static diagnosis - slave signalling static diagnosis and cannot deliver valid data at present -> check operating state at the slave
10
Diagnosis overflow - slave signalling a diagnosis overflow -> check diagnostic data (using ADS-Read, see below) and operating state at the slave
11
Physical fault - physical fault interfering with slave response -> check cables
13
Severe bus fault ->check cabling
14
Telegram fault - slave responding with an invalid telegram -> must not occur
15
Station has no resources -> slave has insufficient resources for the telegram -> check that GSD file is correct
16
Service not activated -> temporary fault when slave ceases data exchange due to a local event, otherwise check whether DP functions are disabled at the slave
17
Unexpected telegram -> can occur temporarily if two PROFIBUS networks are connected together or check whether bus times for the second master are set identically
18
Station ready -> can occur temporarily during StartUp and until the task is started
19
DPV1 StartUp -> occurs temporarily after the DP has started up if there is still data to be sent by DPV1 Write
128
FC310x in slave mode, waiting for data transfer -> slave was parameterized and configured but has not yet received a Data_Exchange telegram
129
FC310x in slave mode, waiting for configuration -> slave was parameterized, but has not yet received a Chk_Cfg telegram
130
FC310x in slave mode, waiting for parameters -> slave was not yet parameterized, waiting for Set_Prm (Lock) telegram