CX1100-0002 power supply LEDs

After switching on, the power supply immediately checks the connected Bus Terminal configuration. Error-free start-up is signalled by the red "I/O ERR” LED being extinguished. If the ”I/O ERR" LED blinks, an error in the area of the terminals is indicated. The error code can be determined from the frequency and number of blinks. This permits rapid rectification of the error.

Display

LED

Meaning

CX1100-0002 power supply LEDs 1:

Power

Power supply

The LED lights up green when the power supply is correct, but red if there is a short circuit.

I/O Run

K-Bus diagnostics

The green LED lights up in order to indicate fault-free operation. "Fault-free" means that the communication with the fieldbus system is also running.

I/O Error

K-Bus diagnostics

The red LED flashes to indicate an error. The red LED blinks with two different frequencies.

The I/O error LED blink code

Fast blinking

Start of the error code

First slow sequence

Error code

Second slow sequence

Error code argument

LEDs for K-Bus diagnosis

Error code

Error code argument

Description

Remedy

Persistent, continuous blinking

 

EMC problems

- Check power supply for overvoltage or undervoltage peaks
- Implement EMC measures
- If a K-Bus error is present, it can be localised by a restart of the power supply (by switching it off and then on again)

1 pulse

0

EEPROM checksum error

Revert to the manufacturer’s setting

1

Code buffer overflow

Insert fewer Bus Terminals. The programmed configuration has too many entries in the table

2

Unknown data type

Software update required for the power supply

2 pulses

0

Programmed configuration has an incorrect table entry

Check programmed configuration for correctness

n (n > 0)

Table comparison (Bus Terminal n)

Incorrect table entry

3 pulses

0

K-Bus command error

- No Bus Terminal inserted
- One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.

4 pulses

0

K-Bus data error, break behind the power supply

Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.

n

Break behind Bus Terminal n

Check whether the Bus End Terminal 9010 is connected.

5 pulses

n

K-Bus error in register communication with Bus Terminal n

Exchange the nth bus terminal

9 pulses

0

Checksum error in Flash program

Revert to the manufacturer’s setting

n (n>0)

Bus Terminal n is not consistent with the configuration that existed when the boot project was created

Revert to the manufacturer's setting which will clear the boot project.

14 pulses

n

nth Bus Terminal has the wrong format

Start the power supply again, and if the error occurs again then exchange the Bus Terminal.

15 pulses

n

Number of Bus Terminals is no longer correct

Start the power supply up again.

16 pulses

n

Length of the K-Bus data is no longer correct

Start the power supply up again.

Error code argument

The number of pulses indicates the position of the last Bus Terminal before the fault. Passive Bus Terminals, such as a power feed terminal, are not included in the count.

In the case of some errors, rectification does not cause the power supply to leave the blink sequence. The power supply can only be restarted by switching its supply voltage off and on again.

Note:

The supply voltage of the power supply unit, which is necessary to supply power to the CX1000 system, must not be interrupted in the middle of operation. Switching off the supply voltage to the power supply unit refers here to the power supply on the power contacts.