CX1100-0002 power supply LEDs
After switching on, the power supply immediately checks the connected Bus Terminal configuration. Error-free start-up is signalled by the red "I/O ERR” LED being extinguished. If the ”I/O ERR" LED blinks, an error in the area of the terminals is indicated. The error code can be determined from the frequency and number of blinks. This permits rapid rectification of the error.
Display
LED
Meaning
CX1100-0002 power supply LEDs 1:
Power
Power supply
The LED lights up green when the power supply is correct, but red if there is a short circuit.
I/O Run
K-Bus diagnostics
The green LED lights up in order to indicate fault-free operation. "Fault-free" means that the communication with the fieldbus system is also running.
I/O Error
K-Bus diagnostics
The red LED flashes to indicate an error. The red LED blinks with two different frequencies.
The I/O error LED blink code
Fast blinking
Start of the error code
First slow sequence
Error code
Second slow sequence
Error code argument
LEDs for K-Bus diagnosis
Error code
Error code argument
Remedy
Persistent, continuous blinking
EMC problems
- Check power supply for overvoltage or undervoltage peaks
- Implement EMC measures
- If a K-Bus error is present, it can be localised by a restart of the power supply (by switching it off and then on again)
1 pulse
0
EEPROM checksum error
Revert to the manufacturer’s setting
1
Code buffer overflow
Insert fewer Bus Terminals. The programmed configuration has too many entries in the table
2
Unknown data type
Software update required for the power supply
2 pulses
0
Programmed configuration has an incorrect table entry
Check programmed configuration for correctness
n (n > 0)
Table comparison (Bus Terminal n)
Incorrect table entry
3 pulses
0
K-Bus command error
- No Bus Terminal inserted
- One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4 pulses
0
K-Bus data error, break behind the power supply
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the Bus End Terminal 9010 is connected.
5 pulses
n
K-Bus error in register communication with Bus Terminal n
Exchange the nth bus terminal
9 pulses
0
Checksum error in Flash program
n (n>0)
Bus Terminal n is not consistent with the configuration that existed when the boot project was created
Revert to the manufacturer's setting which will clear the boot project.
14 pulses
n
nth Bus Terminal has the wrong format
Start the power supply again, and if the error occurs again then exchange the Bus Terminal.
15 pulses
n
Number of Bus Terminals is no longer correct
Start the power supply up again.
16 pulses
n
Length of the K-Bus data is no longer correct
Error code argument
The number of pulses indicates the position of the last Bus Terminal before the fault. Passive Bus Terminals, such as a power feed terminal, are not included in the count.
In the case of some errors, rectification does not cause the power supply to leave the blink sequence. The power supply can only be restarted by switching its supply voltage off and on again.
Note:
The supply voltage of the power supply unit, which is necessary to supply power to the CX1000 system, must not be interrupted in the middle of operation. Switching off the supply voltage to the power supply unit refers here to the power supply on the power contacts.
