Connecting cables and power supply
Notice | |
Incorrect connection procedure Incorrect procedure when connecting the cables and the power supply can cause hardware damage.
The connections are located at the rear in the connection section of the device.
Connecting cables
Make sure that you first ground the panel (see Chapter 4.3.2 Grounding the control panel) and then plug in all data transmission cables.
When connecting the control panel to an industrial PC with UPS output, Beckhoff recommends using this for the connection so that the display is also active in UPS mode. Only one control panel may be connected to the UPS output on the PC.
Connect power supply cable
Cables with a maximum cable cross-section of 1.5 mm2 can be used for connecting the power supply. For long supply lines, use 1.5 mm2 cables to achieve a low voltage drop on the supply line. There should be at least 22 V at the power supply plug of the control panel, so that the panel remains switched on during voltage fluctuations.
Proceed as follows to connect the 24 VDC power supply unit:
- 1. First mount the power supply cable with the 5-pin connection strip without its strain relief housing.
- 2. Plug the voltage connector into the voltage socket on the panel.
- 3. Screw the voltage connector to the voltage socket.
- 4. Connect the panel to your external 24 V power supply.
- 5. Switch on the 24 V power supply.
- 6. Measure the voltage at the 5-pin connection strip of the panel.
- 7. Mount the strain relief housing on the 5-pin connection strip.
- You have connected the power supply cable.