Address Configuration via TwinCAT System Manager
- BX firmware 1.08 or above (see the indication on the BX9000 display after the operating voltage has been switched on).
- all BC9050, BC9020 and BC9120
- from TwinCAT 2.10, build 1322
An operable ADS connection is necessary in order to set the IP address through the System Manager. This can be done via a serial connection or via Ethernet (see chapter Finding the Bus Terminal Controller with the TwinCAT System Manager).
For the BC9x20, DIP switches 9 and 10 must be ON,
for the BC9050 switches 1 and 2 of the two-pin DIP switch must be ON, to enable IP addressing via the System Manager.
The settings made via the System Manager are then applied.
You can now read the current settings with Upload. If the Bus Terminal Controller was configured offline, the Add route button can be used to establish a connection to the Bus Terminal Controller. Edit the required settings, activate the configuration and restart your Bus Terminal Controller with the green TwinCAT icon (shortcut [Ctrl] [F4]). If the Bus Terminal Controller has been assigned a new IP address, you have to re-enter the new route (see chapter Finding the Bus Terminal Controller with the TwinCAT System Manager).