IclA drive at SSB
IclA drive at SSB
Required material:
For the configuration download via ADS, either a BECKHOFF fieldbus master or a free serial port is required.
Reconfiguration example for TwinCAT with FC510x CANopen master card
An example for converting a drive is listed below.
baudratefc510x.wsm
setbaudratefc510x.pro
Example program and configuration on the BX Controller
icla_example.tsm
icla_example.prx
IclA D065 description
The following sections are extracts from the IclA drive manual. They were provided by the company SIG Positec Automation GmbH for the purpose of describing the basic parameters. Further information can be found on the internet at http://www.sig-positec.de.
Hardware and interfaces
IclA drive at SSB 5:
IclA drive connections
IclA drive at SSB 6:
Signal interface
If the emergency stop function is not required, connect pin 2 with pin 8 or 9 (24 VDC).
IclA drive at SSB 7:
Fieldbus connection
Control word 0x6040
The object represents the control word for the device. The control word is used for several control tasks:
Object description
Value description
Index
6040h
Object name
Control word
Data type
Integned16
Subindex
00h, control word
Access
read-write
PDO-Mapping
R_PDO
Bit
Meaning
11..15
Manufacturer specific
not used
9, 10
reserved
8
Stop
Stop motor
7
Reset fault
Reset fault
4..6
Operating mode dependent,
3
Enable operation
Execute operating mode
2
Quick stop (low active)
Breaking with quick stop ramp
1
Disable voltage (low active)
Switch off voltage
0
Switch on
Switch into ready-to-run state
Status word 0x6041
The object describes the current operating state of the device. The status word can be used for the following monitoring functions:
Further details for monitoring travel operation can be found under the keywords "Operating mode, starting", "Operating mode, monitoring" and in the description of the respective operating modes in sections "Manual mode" and "Positioning mode". The bits for device status monitoring are described in section "Diagnostics and trouble shooting".
The control word is represented in the first two bytes of the R_PDOs.
Object description
Value description
Index
6041h
Object name
Status word
Data type
Unsigned16
Subindex
00h, status word
Access
read-only
PDO Mapping
T_PDO
Bit
Meaning
15
Out of security area
0->1: Limit switch position S0 or S1 exceeded
14
Out of drive area
Out of drive area
0->1: Limit switch position D0 or D1 exceeded
12..13
Operating mode-dependent meaning
11
Internal limit active
Out of working area
10
Target reached
Target reached
1->0: New target position transferred
0->1: Requested target position reached or motor standstill after stop request
9
Remote
0: manual mode
1: no manual mode
8
Right out of drive area
Only valid if bit 11 = 1
- 0: Limit switch position W1 exceeded
- 1: Limit switch position W0 exceeded
7
Warning
Warning
6
Switch on disabled
not ready for operation
5
Quick Stop
Quick stop active
4
Voltage disabled
Voltage off
3
Fault
Fault occurred
2
Operation enabled
Operating mode enabled
1
Switched on
Ready for operation
0
Ready to switch on
Ready to switch on
Reference ranges
A valid referencing is defined via three limit switch zones, which have to be within the possible traversing range of the drive. The limit switches protect the drive and the system from damage.
IclA drive at SSB 8:
Reference ranges
Referencing example
The following listing demonstrates the input of the referencing values. The node address of the positioning drive is set to 01hex.
IclA drive at SSB 9:
Listing of the referencing values