Lenze frequency converter at SSB
Frequency converter from Lenze
Required material
For the configuration download via ADS you need a BECKHOFF fieldbus master card or a free serial port.
Lenze description
The following sections are extracts from the Lenze 2175 manual. They were provided by the company Lenze Drive Systems GmbH for the purpose of describing the basic parameters. Further information can be found on the internet at http://www.Lenze.com.
Initial commissioning
Set the power supply for the bus module to internal power supply.
External power supply - internal power supply
(State at Delivery)
For CANopen communication set DIP switch 10 to "ON".
DIP switch
Baud rate DIP switches 7-9
Transfer rate [kbps]
S7
S8
S9
10
ON
ON
OFF
20
ON
OFF
ON
50
OFF
ON
ON
125
OFF
ON
OFF
250
OFF
OFF
ON
500 (default)
OFF
OFF
OFF
1000
ON
OFF
OFF
Lenze frequency converter at SSB 1:
Priority of the DIP switches
DIP switch 6 has the smallest weighting.
Example: Address 3 switches 5 and 6 "ON".
Enabling the communication module
Switch to operating mode 3 for enabling the communication module. This can be achieved via the SSB using the following entry:
Sync telegram
In the default setting, the Lenze drive will send its output PDOs only once it has received a sync telegram from the CAN master. If you set the trans. type to 2, for example, the Lenze drive will send an output PDO after every second sync telegram it receives.
Sample project
bx-lenze.tsm
lenze.prx