DIP switch
The BC9050 and BC9120/BC9020 are equipped with DIP switches. These DIP switches have two functions.
- Addressing mode or setting the IP address
- Configuration mode
Mode one is enabled if Bus Terminals are connected to the K-bus and the Bus Terminal Controller is switched on. Mode two is activated if only the end terminal is connected when the Bus Terminals Controller is switched on.
Mode 1: Addressing mode
DIP switches of the BC9050
Right switch position: ON, switch in left position: OFF.
- DIP switches 1 to 8 edit the last byte of the IP address (the image shows the red DIP switches).
- DIP switches 1 and 2 select the IP address mode (the image shows the blue DIP switches).
DIP1 | DIP2 | Meaning |
off | off | 172.16.21.xxx (xxx corresponds to DIP switch 1-8), subnet mask 255.255.0.0, default gateway 0.0.0.0 |
on | off | BootP (DIP 1-8 all off), BootP & Safe (DIP 1-8 all on) |
off | on | DHCP |
on | on | Configuration via the TwinCAT System Manager |
DIP switches of the BC9020 and BC9120
Right switch position: OFF, switch in left position: ON.
- DIP switches 1 to 8 edit the last byte of the IP address.
- DIP switches 9 to 10 select the IP address mode.
DIP9 | DIP10 | Meaning |
off | off | BC9020 172.16.22.xxx (xxx corresponds to DIP switches 1-8), subnet mask 255.255.0.0, default gateway 0.0.0.0 |
off | on | DHCP |
Mode 2: Configuration mode
In the de-energized Bus Terminal Controller only connect the KL9010 end terminal. Set the DIP switch to the required function, then switch on the Bus Terminal Controller. The function is active as soon as the Controller has booted. Continue as usual. In the BC9020 and BC9120 DIP 9 and 10 must be off, in the BC9050 DIP switches 1 and 2 (2-pin DIP switch) must also be off.
Setting | Meaning | |
BC9050 | BC9020 | |
99 | 99 | Manufacturer’s settings |
98 | 98 | Delete boot project |
97 | 97 | Delete TwinCAT Config |
99 DIP switches
DIP 1 | DIP 2 | DIP 3 | DIP 4 | DIP 5 | DIP 6 | DIP 7 | DIP 8 |
98 DIP switches
97 DIP switches