Overview
Configuration types
The BC9191 Bus Terminal Controllers can be configured in two different ways: DEFAULT CONFIG or TwinCAT CONFIG.
DEFAULT-CONFIG
Fixed addressing BC9191 in the DEFAULT CONFIG:
input/output | Designation | Address | Data type |
Digital_Input_1 | DI 1 | IX 30.0 | Bool |
Digital_Input_12 | DI 2 | IX 30.1 | Bool |
Digital_Input_3 | DI 3 | IX 30.2 | Bool |
Analog_PT_1000 | PT 1000 | IW 2 | Integer |
Analog_Setpoint | Setpoint | IW 6 | Integer |
Analog_Input_1 | AI 1 | IW 10 | Integer |
Analog_Input_2 | AI 2 | IW 14 | Integer |
Analog_Input_3 | AI 3 | IW 18 | Integer |
Analog_Output_1 | AO 1 | QW22 | Integer |
Analog_Output_2 | AO 2 | QW26 | Integer |
Digital_LED_Output | DO 1 | QX 30.0 | Bool |
Relay_Output_2KW | 2 kW2 | QX 30.1 | Bool |
Relay_FAN_1 | FAN 1 | QX 30.2 | Bool |
Relay_FAN_2 | FAN 2 | QX 30.3 | Bool |
Relay_FAN_3 | FAN 3 | QX 30.4 | Bool |
TRIAC_Y1_Output | Y1 | QX 30.5 | Bool |
TRIAC_Y2_Output | Y2 | QX 30.6 | Bool |
KL6581.InData | CAN | IB32 … IB43 | 12 bytes |
KL6581.OutData | CAN | QB32 … QB43 | 12 bytes |
Further connected terminals start with the addresses IB44 or Qb44 | |||
Fixed addressing BC9191-0100 in the DEFAULT-CONFIG:
KL6041.InData | RS 485 | IB32 … IB55 | 23 bytes |
KL6041.OutData | RS 485 | QB32 … QB55 | 23 bytes |
Further connected terminals start with the addresses IB 56 or QB 56 | |||
TWINCAT-CONFIG
In the TWINCAT CONFIG the integrated inputs/outputs and connected Bus Terminals can be freely linked (TwinCAT System Manager file required). The configuration is transferred to the BC9191 with the System Manager via ADS.
For the TwinCAT Config (TC file) you need a PC with TwinCAT 2.10 build 1322 or higher.
OThe System Manager of the TwinCAT 2 program can be used to parameterize the following properties:
- Variable I/O mapping
- PLC settings
- K-bus settings
The configuration can be transferred to the BCx9191 via ADS protocol.
The TwinCAT configuration can be used to link variables, I/Os and data.
In addition, the TwinCAT configuration can be used to parameterize special behavior, for example whether data are preserved or set to "0" in the event of an FK-Bus error.
The internal clock of the BC9191 can be set via a tab in the System Manager.