FB_BC9191FanCoil

Application
This function block maps a 3-stage fan. The three stages are switched via the control value (0...100%) of the heating or cooling controller. Furthermore there is a possibility to manually override the fan controller via the iStageManual or bStageUp or bStageDown input. A minimum switch-on time can be set via the udiSecMINPowerOnTime input, which is then valid for each stage.
VAR_INPUT
Name : Type
bSetDefault : BOOL;
bEnable : BOOL;
eCtrlFct : E_BC9191CtrlFct;
rY_C : REAL;
rY_H : REAL;
bStageUp : BOOL;
bStageDown : BOOL;
iStageManual : INT;
bReset : BOOL;
bSetDefault: If the variable is TRUE, the default values of the VAR_IN_OUT variables are adopted.
bEnable: The function block is activated if the variable bEnable is TRUE. No fan stage is activated with a FALSE.
eCtrlFct: This input is connected to the eCtrlFct output of the FB_BC9191FctSelection. This information is important in order to know whether the plant is in heating or cooling mode. In automatic mode, the fan stages are only activated if
- the system is in heating mode and according to the control deviation the request for heating is active or
- the system is in cooling mode and according to the control deviation the request for cooling is active.
rY_C: Input for the control value from the cooling controller.
rY_H: Input for the control value from the heating controller.
bStageUp: Local adjustment of the fan stage, stepwise increase by push button.
bStageDown: Local adjustment of the fan stage, stepwise decrease by push button.
iStageManual: The manual fan stage can/is set centrally via this input.
iStageManual: = 0 corresponds to fan stage OFF
iStageManual: = 1 corresponds to fan stage AUTO
iStageManual: = 2 corresponds to fan stage01 active
iStageManual: = 3, corresponds to fan stage02 active
iStageManual: = 4, corresponds to fan stage03 active
bReset: Acknowledge input in case of a fault or an incorrect parameter.
VAR_OUTPUT
Name : Type
bStageOff : BOOL;
bStageAuto : BOOL;
bStage01 : BOOL;
bStage02 : BOOL;
bStage03 : BOOL;
bFanCoilActive : BOOL;
bPresence : BOOL;
byState : BYTE;
byError : BYTE;
udiSecRT_MINPowerOnTime : UDINT;
udiRT_TimePeriod : UDINT;
bInvalidParameter : BOOL;
bStageOff: TRUE, fan stages are switched off.
bStageAuto: TRUE, fan controller is in automatic mode.
bStage01: TRUE, fan stage01 active.
bStage02: TRUE, fan stage02 active.
bStage03: TRUE, fan stage03 active.
bFanCoilActive: TRUE if one of the three fan stages is active. This output can be/is used to enable controllers in order to avoid a build up of heat or cold.
bPresence: TRUE means that presence was detected via the bStageUp, bStageDown or iStageManual inputs.
byState: Indicates the state of the fan controller.
byState.0:= Function block is activated
byState.3:= Manual fan stage setting is active
byState.4:= bReset
byState.5:= Fan stage01 active
byState.6:= Fan stage02 active
byState.7:= Fan stage03 active
byError: Output of the errors as byte.
byError.1:= bInvalidParameter
udiSecRT_MINPowerOnTime: Indicates the remaining time of the minimum switch-on time.
udiRT_TimePeriod: Indicates the remaining time of the manual override.
bInvalidParameter: Indicates that an incorrect input parameter is present. bInvalidParameter must be acknowledged with bReset.
VAR_IN_OUT
Name : Type Persistent Default
rValvePositionH_Stage01 : REAL; X 0 %
rValvePositionH_Stage02 : REAL; X 21 %
rValvePositionH_Stage03 : REAL; X 76 %
rValvePositionC_Stage01 : REAL; X 0 %
rValvePositionC_Stage02 : REAL; X 21 %
rValvePositionC_Stage03 : REAL; X 76 %
udiSecMINPowerOnTime : UDINT; X 120 sec
iFctModeFanCoil : INT; X 3
udiTimePeriod : UDINT; X 60 min
rValvePositionH_Stage01: Limit value of the control value of the heating controller from which fan stage01 is switched on.
rValvePositionH_Stage02: Limit value of the control value of the heating controller from which fan stage02 is switched on.
rValvePositionH_Stage03: Limit value of the control value of the heating controller from which fan stage03 is switched on.
rValvePositionC_Stage01: Limit value of the control value of the cooling controller from which fan stage01 is switched on.
rValvePositionC_Stage02: Limit value of the control value of the cooling controller from which fan stage02 is switched on.
rValvePositionC_Stage03: Limit value of the control value of the cooling controller from which fan stage03 is switched on.
udiSecMINPowerOnTime: Minimum switch-on time that a fan must run for in a stage before switching to a different stage or switching off. Input in seconds (e.g. 120 corresponds to 120 s).
iFctModeFanCoil: The user has the possibility to activate the fan controller for heating mode or cooling mode or both modes via the valence of this variable. Valid values are 1, 2 or 3. Other values are invalid and bInvalidParameter is set to TRUE.
Cooling | Heating | Valence |
|---|---|---|
0 | 1 | 1 (= fan controller active in heating mode) |
1 | 0 | 2 (= fan controller active in cooling mode) |
1 | 1 | 3 (= fan controller active in heating mode and cooling mode) |
udiTimePeriod: Timeframe during which the manual override is active in case of presence. Specified in minutes