Diagnostic LEDs
The Bus Terminal Controller has LEDs that indicate the status. The row of LEDs on the left describes the status of the fieldbus and of the PLC. The row of LEDs on the right indicates the supply voltage and the K-Bus state.
POWER LEDs for diagnostics of power supply
LED (Power LEDs) | Meaning |
LED Us | LED off: Bus Terminal Controller has no 24 VDC voltage |
LED Up | LED off: No power supply 24 VDC connected at the power contacts |
LEDs for K-Bus diagnostics
LED RUN | LED off: no K-bus update |
LED ERR | LED off: No error |
Error codes for K-Bus diagnosis
Error code | Error code argument | Description | Remedy |
0 | - | EMC problems |
1 | 0 | EEPROM checksum error | Enter factory settings with the KS2000 configuration software |
1 | Code buffer overflow | Insert fewer Bus Terminals. The programmed configuration has too many entries in the table | |
2 | Unknown data type | Software update required for the BX Controller | |
2 | - | reserved | - |
3 | 0 | K-bus command error |
4 | 0 | K-bus data error, break behind the BX Controller | Check whether the n+1 Bus Terminal is correctly connected; replace if necessary. |
n | Break behind Bus Terminal n | Check whether the KL9010 Bus End Terminal is connected | |
5 | n | K-bus error in register communication with Bus Terminal n | Exchange the nth Bus Terminal |
6 | 0 | Error at initialization | Replace BX Controller |
1 | Internal data error | Perform a hardware reset on the BX Controller (switch off and on again) | |
2 | DIP switch changed after a software reset | Perform a hardware reset on the BX Controller (switch off and on again) | |
7 | 0 | Note: cycle time was exceeded | Warning: the set cycle time was exceeded. This indication (flashing LEDs) can only be cleared by booting the BX Controller again. |
9 | 0 | Checksum error in Flash program | Transmit program to the BX again |
1 | Incorrect or faulty library implemented | Remove the faulty library | |
10 | n | Bus Terminal n is not consistent with the configuration that existed when the boot project was created | Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional. |
14 | n | nth Bus Terminal has the wrong format | Start the BX Controller again, and if the error occurs again then exchange the Bus Terminal. |
15 | n | Number of Bus Terminals is no longer correct | Start the BX Controller again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software |
16 | n | Length of the K-bus data is no longer correct | Start the BX Controller again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software |
LED bus - fieldbus diagnostics
LED BUS OFF | LED CONNECT | LED OVERFLOW | Meaning |
on | off | off | No fieldbus connected, Bus Terminal Controller searches for the baud rate, 24 V DeviceNet voltage missing |
flashes | Blink | off | Stopped, no error, Bus Terminal Controller searches for the baud rate |
off | on | off | No error |
off | flashes | off | Bus OFF, wrong baud rate |
off | off | on | Warning Level |
LED PLC - PLC diagnostics
LED | Meaning |
PLC LED | LED on: PLC running |