Diagnostic LEDs
The Bus Terminal Controller has LEDs that indicate the status. The row of LEDs on the left describes the status of the fieldbus and of the PLC. The row of LEDs on the right indicates the supply voltage and the K-Bus state.
Diagnostic LEDs 1:
Diagnostic LEDs
POWER LEDs for diagnostics of power supply
LED (Power LEDs)
Meaning
LED Us
LED off: Bus Terminal Controller has no 24 VDC voltage
LED Up
LED off: No power supply 24 VDC connected at the power contacts
LEDs for K-Bus diagnostics
LED (Power LEDs)
Meaning
LED RUN
LED off: no K-bus update
LED on, flashes: K-bus running
LED ERR
LED off: No error
LED flashes: see K-Bus error code
Error codes for K-Bus diagnosis
Error code
Error code argument
Remedy
0
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart of the coupler (by switching it off and then on again)
1
0
EEPROM checksum error
Enter factory settings with the KS2000 configuration software
1
Code buffer overflow
Insert fewer Bus Terminals. The programmed configuration has too many entries in the table
2
Unknown data type
Software update required for the BX Controller
2
reserved
3
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4
0
K-bus data error, break behind the BX Controller
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the KL9010 Bus End Terminal is connected
5
n
K-bus error in register communication with Bus Terminal n
Exchange the nth Bus Terminal
6
0
Error at initialization
Replace BX Controller
1
Internal data error
Perform a hardware reset on the BX Controller (switch off and on again)
2
DIP switch changed after a software reset
7
0
Note: cycle time was exceeded
Warning: the set cycle time was exceeded. This indication (flashing LEDs) can only be cleared by booting the BX Controller again.
Remedy: increase the cycle time
9
0
Checksum error in Flash program
Transmit program to the BX again
1
Incorrect or faulty library implemented
Remove the faulty library
10
n
Bus Terminal n is not consistent with the configuration that existed when the boot project was created
Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional.
14
n
nth Bus Terminal has the wrong format
Start the BX Controller again, and if the error occurs again then exchange the Bus Terminal.
15
n
Number of Bus Terminals is no longer correct
Start the BX Controller again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16
n
Length of the K-bus data is no longer correct
LED bus - fieldbus diagnostics
LED BUS OFF
LED CONNECT
LED OVERFLOW
Meaning
on
off
off
No fieldbus connected, Bus Terminal Controller searches for the baud rate, 24 V DeviceNet voltage missing
flashes
Blink
off
Stopped, no error, Bus Terminal Controller searches for the baud rate
off
on
off
No error
off
flashes
off
Bus OFF, wrong baud rate
off
off
on
Warning Level
LED PLC - PLC diagnostics
LED
Meaning
PLC LED
LED on: PLC running
LED off: PLC stopped