Master parameterization
Configuration at a Rockwell/Allen Bradley controller
The BX5200 and BC5250 have two configuration types. In the default configuration, the coupler is supplied and has the following DeviceNet characteristics:
- AutoBaud
- 8 bytes inputs DN (from address %IB1000) - these are then the outputs on the master
- 8 bytes outputs DN (from address %QB1000) - these are then the inputs on the master
If it is necessary to change the preset data, a special library is required.
In the TwinCAT configuration, it is possible with the aid of the System Manager to set the DN Slave-specific characteristics. The library is not to be used for the default configuration.
The EDS file and the icon file are always integrated in the RSNetworx with the EDS wizard:

Finally the DeviceNet network is searched with the Network-Browse for the nodes within the network. If the BC/BX are correctly connected to the network with the correct baud rate, they are recognized and correspondingly displayed:

Double-clicking the icon opens the configuration dialog for the units.
Below Parameter appear the I/O data lengths that are currently set at the BC/BX.

The produced and consumed data should always be considered from the point of view of the network, i.e. BC/BX produce data for DeviceNet and consume data from DeviceNet.
- The data produced are thus the input data of the master, i.e. data that are sent from the BC/BX to the master: BC/BX Produced Size = Input Size Scanner
- The data consumed are the output data of the master, i.e. data that are sent from the master to the slave: BC/BX Consumed Size = Output Size Scanner
A double-click on the Scanner/DeviceNet Master icon opens the configuration dialog. The recognized modules appear in the Available Devices list and must now be added to the Scanlist.

A double-click on the icon of the device to be configured opens the dialog for setting the I/O data lengths

- BC/BX Produced-Size = Input-Size
- BC/BX Consumed-Size = Output-Size
Furthermore, it must be ensured that the I/O operation mode selected here corresponds to the I/O mode selection.
The Interscan Delay, that is the time between each I/O cycle, must be selected according to the requirements of the BC/BX with respect to the size of the PLC program and the I/O data lengths.