Diagnostic LEDs
The Bus Coupler features status indicator LEDs. The row of LEDs on the left describes the status of the fieldbus and of the PLC. The row of LEDs on the right indicates the supply voltage and the K-Bus state.
Diagnostic LEDs 1:
LEDs
LEDs for power supply diagnostics
LED (Power LEDs)
Meaning
LED Us
LED off: Bus Coupler has no voltage 24 VDC
LED Up
LED off: No 24 VDC power supply connected to the power contacts
LEDs for K-Bus diagnostics
LED (Power LEDs)
Meaning
LED RUN
LED off: no K-Bus update, LED on, flashing: K-bus running
LED ERR
LED off: no error, LED flashing: see K-Bus error code
K-Bus error code diagnostics
Error
code
Error
argument
Remedy
0
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart of the coupler (by switching it off and then on again)
1
0
EEPROM checksum error
Enter factory settings with the KS2000 configuration software
1
Code buffer overflow
Insert fewer Bus Terminals. Too many entries in the table for the programmed configuration
2
Unknown data type
Software update required for the Bus Coupler
2
Reserve
3
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4
0
K-bus data error, break behind the Bus Coupler
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the KL9010 Bus End Terminal is connected
5
n
K-bus error in register communication with Bus Terminal n
Exchange the nth Bus Terminal
6
0
Error at initialization
Exchange Bus Coupler
1
Internal data error
Perform a hardware reset on the Bus Coupler (switch off and on again)
2
DIP switch changed after a software reset
7
0
Note: cycle time was exceeded
Warning: the set cycle time was exceeded. This indication (flashing LEDs) can only be cleared by booting the Bus Coupler again.
Remedy: increase the cycle time
9
0
Checksum error in Flash program
Re-transfer the program to the Bus Terminal Controller
1
Incorrect or faulty library implemented
Remove the faulty library
10
n
Bus Terminal n is not consistent with the configuration that existed when the boot project was created
Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional.
14
n
nth Bus Terminal has the wrong format
Start the Bus Coupler again, and if the error occurs again then exchange the Bus Terminal
15
n
Number of Bus Terminals is no longer correct
Start the Bus Coupler again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16
n
Length of the K-bus data is no longer correct
LED bus - fieldbus diagnostics
LED
Meaning
LED RUN
no fieldbus connected, Bus Coupler searches for baud rate
LED BF
error flashing - error type - display
LED DIA
Bus Coupler has found baud rate, waiting for config and parameter data
LED RUN
LED BF
LED DIA
Meaning
off
off
off
on
on
on
on
on
off
on
off
off
no error, coupler in data exchange
on
off
flashing
error, see error code
LED PLC - PLC diagnostics
LED
Meaning
PLC LED
LED on: PLC running, LED off: PLC stopped