Parametering
Activation
The temperature compensation can be switched on in the axis parameter list [AXIS] of the related axis by P-AXIS-00271:
kopf.achs_nr 1
# temperature compensation on/off
lr_param.temp_comp 1Beside this for TwinCAT the compensation also can be selected via ADS-write access in the GEO task (Port 551).
TEMPC::is_active IGrp = 0x20300, IOffs = 0x10041Effectiveness
The temperature compensation is enabled, if:
- it is activated for an axis and
- the axis is referenced.
Reference measuring
To be able to define the parameters of the temperature compensation at first a reference measuring with an external position measuring system must be done. During this process for varying temperatures the deviations of the axis positions between internal and external measuring system are determined.
Determination of parameters
The parameters reference position, shift and coefficient can be taken from the measuring curve. Out of this later the values at a given temperature can be determined. From the measured temperature curves non-measured temperatures can be defined via inter- or extrapolation.
If the selected reference position is the virtual intersection point of the approximated linear curve, the shift depends on the temperature. In this case, for the varying temperatures only the coefficient must be adjusted new.
Influence of temperature
The individual parameters can be adjusted by the PLC depending on the current temperature. For this a specific temperature signal (sensor) is transmitted to the PLC.
From this signal the PLC derives the parameters.
Changing of parameters
Via download of the axis parameter list the individual parameters can be changed.
kopf.achs_nr 1
# reference position
lr_param.temp_comp_position_0 100 [0.1µm]
# reference offset
lr_param.temp_comp_offset_0 40 [0.1µm]
lr_param.temp_comp_coefficient 4000 [µm/m]
Beside the download there also exists a read/ write manipulation for parameters via direct ADS access in the GEO task (Port 551). For example, the first axis can be addressed via following index group and index offset:
TEMPC::coefficient IGrp = 0x20300, IOffs = 0x10043
TEMPC::offset_0 IGrp = 0x20300, IOffs = 0x10044
TEMPC::position_0 IGrp = 0x20300, IOffs = 0x10045
Monitoring distribution of compensation values
For every interpolation cycle the compensation values are re-calculated. If the change per cycle exceeds the given maximum axis acceleration, this change can be output via a filter in several cycles.
For this in the axis parameter list the number of cycles of the sin²- filter can be set. Per default the value is one cycle.
kopf.achs_nr 1
#Number of cycles of the sin²-filter
lr_param.temp_comp_n_cycles 20
Display of compensation
TEMPC::actual_offset IGrp = 0x20300, Ioffs = 0x10042Display of axis position
During active temperature compensation the normal command positions and current positions of the axis are displayed without any manipulation.