Basic Principles
In general, two TwinCAT software modules are required for controlling the AX5000: TwinCAT NC PTP and TwinCAT PLC.
TwinCAT NC is a closed software module whose features the user can only influence via parameters. The TwinCAT NC parameters can be set in the TwinCAT System Manager.
TwinCAT PLC is an interpreter for a program code which the user creates in the PLC Control development environment.
Structure of TwinCAT NC PTP
TwinCAT NC has 2 tasks:
The SPP task is responsible for planning the requested traversing task. The SEC task is responsible for maintaining this path.
The traversing task leaves the PLC in the direction of the ADS router with destination NC-Task 1 SVB (NC task 1 SPP). The router relays the telegram to this task.
Basic Principles 1:
The NC accepts or rejects the message. The response arrives back at the calling block in the PLC via the same route. Instructions are issued based on blocks contained in TCMC.lib. Once the NC has accepted the instruction, the system tries to calculate a solution taking into account the boundary conditions (max. velocity, acceleration, deceleration, and jerk).
Basic Principles 2:
If a solution exists, a table containing the position (s) velocity (v), acceleration/deceleration (a) and jerk (j) for the whole travel time within the sampling time of the SEC task is transferred to the SEC.
If no solution exists, the system deviates downwards based on maximum jerk, maximum acceleration, and maximum velocity (in this order).
Actual and set values shown in the diagram are served by the 1_Enc axis and 1_Drive axis components.
Basic Principles 3:
Since the AX5000 is known to the system as a slave, linking can take place automatically if required. In the event of problems the link can be checked by the user.
NC / AX5000 link specification
NC set values
AX5000 set values
NC actual values
AX5000 Actual values
axis n_Drive / outputs/axis n_DriveOut / nOutData1
MDT n / position set value (option)
axis n_Enc / inputs / axis 1_Enc_In / nInData1
AT n / actual position value sensor 1
axis n_Drive / outputs/axis n_DriveOut / nOutData2
MDT n / velocity set value
axis n_Drive / outputs/axis n_DriveOut / nCtrl1
MDT n / master control word (Hi-byte)
axis n_Drive / inputs/axis n_DriveIn / nStatus1 & nStatus2
AT n / drive status word
axis n_Drive / inputs/axis n_DriveIn / nStatus4
WcState' / WcState
Structure of the AX5000 slave in the TwinCAT System Manager.
The AX5000 parameter management is based on the Sercos profile. The parameter description is based on a standardised structure.
Element 1: IDN (required)
IDN description. Bit 15 distinguishes between standard parameters (S-0-nnnn) and manufacturer-specific parameters (P-0-mmmm).
Bit
Value
0
S-0-nnnn (standard parameter)
1
P-0-mmmm (manufacturer-specific parameter)
12-14
product data (manufacturer-specific)
0-11
0...4095
block number
Element 2: Name (optional)
The name includes a brief description of the parameter in text form.
Byte 1,2
Byte 3,4
Byte 5, max. 64
Current length of the name in characters (1 character = 1 byte)
maximum length of the name in characters (1 character = 1 byte)
name (max. 60 characters)
Element 3: Attributes (required)
This double word describes the IDN properties (write protection, data type, decimal places).
Bit
Value
Reserved
30
1 / 0
Write protection in Op phase / no write protection in Op phase
29
1 / 0
Write protection in SaveOp phase / no write protection in SaveOp phase
28
1 / 0
Write protection in PreOp phase / no write protection in PreOp phase
24-27
0000 - 1111
Number of decimal places for floating point numbers
23
Reserved
20-22
Value
Data type
Represented as
000
Binary
Binary
001
Unsign Integer
Unsigned decimal
010
Sign Integer
Sign decimal
011
Unsign Integer
Hexadecimal
100
Character string
Text
101
Unsign Integer
IDN
110
Floating point number
Sign decimal with exponent
111
Reserved
19
1 / 0
Command / Parameter. A command executes an assigned function
16-18
000
Reserved
001
Length: 2 bytes
010
Length: 4 bytes
011
Length: 8 bytes
100
101
110
111
Element 4: Units (optional)
Byte 1,2
Byte 3,4
Byte 5, max. 16
Physical units max. 12 characters.
Element 5 & 6: Min. & max. values (optional)
The limits for the associated IDN entries are specified here.
Element 7: Value (required)
Four different memory lengths are used.
With this variables IDN structure different data types can be stored, displayed and managed. These parameters specify the controller characteristics:
These data are not stored in the controller but in the TwinCAT configuration. The following diagram illustrates how the data configured in the TcDriveManager are stored.
Basic Principles 4:
Once the parameters have been set in the TcDriveManager they can be transferred to the Startup list.
After the data have been transferred to the Startup list, they are downloaded to the controller after configuration has been saved and TwinCAT has been restarted.
Some parameter can simply be transferred temporarily into the controller RAM. These parameters are lost during a restart or a power failure.
Basic Principles 5:
Inactive write protection is a prerequisite for a successful download. Write protection is set for some parameters when the EtherCAT slave reaches the SafeOP or OP state.
An attempt to change a read-only parameter results in the following error message.
Basic Principles 6:
In this case the only available procedure is as follows:
  1. Parameter transfer to the Startup list
  2. Saving the configuration
  3. Restart TwinCAT