X06: Digital I/Os
CAUTION
Destruction of the AX5000!
This connector is not designed for external power supply. It is supplied via the 24 V supply (periphery) of connector X03.
I/O plug connector without LEDs
ZS4500-2006
X06: Digital I/Os 1:
I/O plug connector with LEDs
ZS4500-2007 (optional)
X06: Digital I/Os 2:
ZS4500-2008 (optional)
X06: Digital I/Os 3:
Terminal point
Signal
Output current
Wire cross-section
24
Power supply for the external sensors (switches/initiators)
(Up 24 VDC +)
max. 1 A
Max. 1.5 mm²
0
Input 0
1
Input 1
2
Input 2
3
Input 3
4
Input 4
5
Input 5
6
Input 6
7
Input 7 or output (configurable)
(Up 24 VDC +)
max. 0.5 A
0 V
GND (-)
Beckhoff servo drives of the AX5000 series have eight (0–7) digital inputs. The input 7 can be configured to an output. All inputs and outputs can be freely assigned to channel A or B. The information provided in parameter P-0-0801 shows the status of the digital inputs. These can be transferred to the cyclic interface and provided in the PLC / NC.
There are two different ways to configure input 7 as an output:
Whether the signal source comes from the servo drive or the PLC is indicated by parameter P-0-0801.
Voltage level
State
-3 V…5 V
0 or “false”
15 V…30 V
1 or “true”
X06: Digital I/Os 4:
Configuration of the connector signal inputs:
The signal inputs can be configured with the following functions:
P-0-0251, P-0-0400, P-0-0401, P-0-0402, P-0-0800, P-0-0801, P-0-0802.
For further information please refer to the documentation for the
S- and P-parameters of the AX5000 servo drive series.