X01: Connection to the supply network
NOTICE
X01: Connection to the supply network 1:
UL approval!
If you intend to operate an AX5000 in a region that requires UL approval, please refer to the chapter “Guidelines and Standards”.
Voltage systems ranging from single-phase 100 VAC to three-phase 480 VAC can be connected to the wide-range voltage input of the AX5000. In single-phase systems the mains phase is connected to terminal point L1 and the neutral conductor to terminal point L3/N.
X01: Connection to the supply network 2:
Terminal point
Connection
Wire cross-section
Tightening torque of the terminal points
3-phase
1-phase
L1
Phase L1
Phase L1
Max. 6 mm²
0.5 Nm…0.6 Nm
L2
Phase L2
not used
L3/ N
Phase L3
Neutral conductor
PE
Protective earth
Protective earth
Connection to the standard supply network (TT / TN) with grounded center
1-phase 100 -10% .- 240 +10% VAC, 50/60 Hz
3-phase 100 -10% .- 480 +10% VAC, 50/60 Hz
X01: Connection to the supply network 3:
X01: Connection to the supply network 4:
Connection to an IT network (100…240 V) without an isolating transformer
Notice
EMC law in Europe!
Due to electromagnetic emission, in Europe the AX5000 must be operated on an IT network in conjunction with an isolating transformer.
X01: Connection to the supply network 5:
Connection to other types of network (100…240 V) without isolating transformer
X01: Connection to the supply network 6:
X01: Connection to the supply network 7:
Connection to other types of network (100…480 V) with isolating transformer
Notice
Destruction of the AX5000!
The use of an isolating transformer is necessary in every case for asymmetric grounded or non-grounded 100…480 V networks.
100…480 V isolating transformer
240…480 V isolating transformer
X01: Connection to the supply network 8: