Electrical data - servo drive (AX5101 - AX5140)
1-phase connection
Technical data
AX5101
AX5103
AX5106
Nominal output current
1.5 A
3 A
4.5 A
Smallest parameterizable channel peak current at full current resolution
0.35 A
1 A
1 A
Peak output current 1)
4.5 A
7.5 A
13 A
Nominal supply voltage
1 x 100-10% - 240+10% VAC
Max. DC link voltage 2)
875 VDC
Nominal apparent power S1 operation (selection)
120 V
230 V
0.3 kVA
0.6 kVA
0.6 kVA
1.2 kVA
0.94 kVA
1.8 kVA
Power loss 3)
35 W
50 W
85 W
Continuous braking power (internal braking resistor)
50 W
50 W
150 W
Max. braking power (internal braking resistor)
14 kW
Min. braking resistor (external braking resistor)
47 Ω
Max. braking power (external braking resistor)
15 kW
DC link capacitance
235 µF
SCCR value
18 kA
1) Irms for max. 7 s, at a clock frequency of 8 kHz (IDN P-0-0001)
2) Info: The higher the power consumption in the DC link, the more the DC link voltage drops
3)
S1 Operation incl. power supply, without brake chopper
3-phase connection
Electrical data
AX5101
AX5103
AX5106
AX5112
AX5118
AX5125
AX5140
1.5 A
3 A
6 A
12 A
18 A
25 A1)
40 A
0.35 A
1 A
1 A
6 A
12 A
12 A
18 A
Peak output current 3)
4.5 A
7.5 A
13 A
26 A 4)
36 A
50 A
80 A
3 x 100-10% - 480+10% VAC2)
875 VDC
120 V
230 V
400 V
480 V
0.3 kVA
0.6 kVA
1.0 kVA
1.2 kVA
0.6 kVA
1.2 kVA
2.1 kVA
2.5 kVA
1.2 kVA
2.4 kVA
4.2 kVA
5.0 kVA
2.5 kVA
4.8 kVA
8.3 kVA
10 kVA
3.4 kVA
7.2 kVA
12.5 kVA
15 kVA
4.8 kVA
10 kVA
17.3 kVA
20.8 kVA
8.3 kVA
16 kVA
28 kVA
33 kVA
Power loss 5)
35 W
50 W
85 W
160 W
255 W
340 W
510 W
Max. continuous braking power (internal braking resistor)
50 W
50 W
150 W
90 W
200 W
200 W
150 W
Braking power (internal braking resistor)
14 kW
26 kW
26 kW
26 kW
47 Ω
47 Ω
47 Ω
30 Ω
22 Ω
22 Ω
22 Ω 6)
15 kW
15 kW
15 kW
23.5 kW
32 kW
32 kW
32 kW
DC link capacitance
235 µF
470 µF
940 µF
1175 µF
1485 µF
SCCR value
18 kA
1)cULus = 24 A
2)
cULus = AX5118 and AX5125 = 3 x 480 VAC ± 10%
3)
Irms for max. 7 s, if clock frequency 8 kHz (IDN P-0-0001)
4) Irms for max. 7 s, if rotating field frequency ≥ 1.5 Hz
   Irms for max. 1 s, if rotating field frequency < 1.5 Hz
5)
S1 operation incl. power supply unit, without brake chopper
6) Braking resistor < 22 Ω - > Please ask our support