External protection for individual devices, UL-compliant
| The AX5000 may only be connected to a standard supply network with an grounded center, whereby the voltage to ground may be max. 277 V. |
Use UL fuses of class RK5 for the mains-side protection.
The integrated protection against short circuit is no substitute for the external protection of the supply network. The protection of the supply network must comply with the vendor's specification and the national and international regulations and laws.
Can be used in power supply systems with a maximum current carrying capacity of 18000 A at 480 V. For alternatives to UL Class RK5 fuses, be sure to refer to UL Standard UL 508 A, Chapter SB4.2.3, Exception No. 1. For further questions regarding UL fuses, please contact the appropriate certificate authority.
SB4.2.3 A high fault short circuit current value for a motor controller, overload relay or combined motor controller as specified in SB4.2.2 (a) or (c) may be used as the short circuit current value of the component if the specified branch circuit protection device is provided.
Exception 1: Where the specified BCPD is a Class CC, G, J, L, RK1, RK5, or T fuse with respect to the high fault SCCR, a fuse of a different class may be used at the same high fault rating, provided the Ip let-through current and I2t of the new fuse are not greater than that of the specified fuse. See table SB4.2 for maximum let-through currents (Ip) and I2t.
Single-phase
| AX5101 | AX5103 | AX5106 | AX5201 | AX5203 | AX5206 |
AC supply max. *) | 6 A | 12 A | 20 A | 12 A | 20 A | 20 A |
24 V DC supply max. | 3 AT | |||||
Braking resistor | electronic | |||||
Three-phase
| AX5112 | AX5118 | AX5125 | AX5140 |
AC supply max. *) | 20 A | 35 A | 45 A | 80 A |
NOTICE | ||
![]() | AX5112! Protection only by UL-approved fuses with a rated current of 20 A and 480 V min. | |
Internal protection, UL-compliant
Circuit | Fuse |
24 V system voltage | 3.4 AF |
24 V peripheral voltage | electronic |
External drive system protection
Rule of thumb: | Determine the rated sum currents of the devices, multiply with the correction factor and round up to the next higher standard level. |
Example: | 1 x AX5103 + 2 x AX5201 + 2 x AX5203 |
NOTICE | ||
![]() | Special requirements for a drive system Please consult our applications department with respect to the special requirements for a drive system with UL approval. | |
Residual current circuit breaker
Servo drives with built-in mains filters generate a small leakage current (fault current) due to the capacitors in the filter. This fault current is responsible for malfunctions in standard residual current circuit breakers. For this reason so-called all-current sensitive residual current circuit breakers must be used, which also take into account DC currents.