Connection example - module AX5901 and AX5911 (AX Bridge)
This connection technology enables a safe system to be set up very quickly. The modules are attached to plug contacts X01, X02 and X03, the relevant sliders are pushed to the left and screwed tight. According to CE, the current carrying capacity of the power busbars of the AX-Bridge is limited to 85 A.
Risk of injury due to electric shock! Move all busbar sliders to the left limit stop in order to ensure full current-carrying capacity. Then tighten all screws with a torque of 2.2 Nm. |
Personal injuries! Please ensure that the connection cable for the AX5901 power supply module is adequately dimensioned. The dimensioning depends on the rated sum current and must comply with EN 60204-1. A 3-phase connection must be used if the rated sum current exceeds 9 A. |
AX5901 (AX520x and AX5101 - AX5125)
Terminal points | Conductor design | Max. conductor cross-section | Tightening torque |
L1-L3, PE | solid wire | 10 mm2, AWG 7 | 2.2 Nm |
stranded wire with ferrule | 16 mm2, AWG 5 | 2.2 Nm | |
stranded- / multi-wire | 25 mm2, AWG 3 | 2.2 Nm | |
Us, Up, GND |
| 16 mm², AWG 5 | 2.2 Nm |
AX5902 (AX5140)
L1-L3, PE | solid wire | 16 mm2, AWG 5 | 3.2 ± 0.8 Nm |
stranded wire with ferrule | 16 mm2, AWG 5 | 3.2 ± 0.8 Nm | |
stranded- / multi-wire | 25 mm2, AWG 3 | 3.2 ± 0.8 Nm | |
Us, Up, GND |
| 16 mm², AWG 5 | 3.2 ± 0.8 Nm |
