Connection example - module AX5901 and AX5911 (AX-Bridge)
This connection technology enables a safe system to be set up very quickly. The modules are attached to plug contacts X01, X02 and X03, the relevant sliders are pushed to the left and screwed tight. According to CE, the current-carrying capacity of the power busbars of the AX-Bridge is limited to 85 A.
CAUTION
Risk of injury due to electric shock
Move all busbar sliders to the left limit stop in order to ensure full current-carrying capacity. Then tighten all screws with a torque of 2.2 Nm.
CAUTION
Personal injuries
Please ensure that the connection cable for the AX5901 power supply module is adequately dimensioned. The dimensioning depends on the rated sum current and must comply with EN 60204-1.
The supply connection is established as described in chapters 5.2.1 and 5.2.2.
Connection example - module AX5901 and AX5911 (AX-Bridge) 1:
Data of the terminal points
Terminal point
Wire design
max. wire cross-section
Tightening torque
L1-L3, PE
solid wire
10 mm²; AWG 7
2.2 Nm
L1-L3, PE
stranded wire with ferrule
16 mm²; AWG 5
2.2 Nm
L1-L3, PE
stranded / multi-wire
25 mm²;AWG 3
2.2 Nm
Us, Up, GND
16 mm²; AWG 5
2.2 Nm