External fuse protection for individual devices, UL-compliant
External fuse protection for individual devices, UL-compliant 1:
External fuse protection of the supply network
The integrated protection against short circuit is no substitute for the external fuse protection of the supply network. The fuse protection of the supply network must comply with the manufacturer's specifications and the national and international regulations and laws.
Use UL circuit breakers of class RK5 for the mains-side fuse protection.
Can be used in supply networks with a maximum current-carrying capacity of 18000 A at 480 V AC. For alternatives to UL Class RK5 circuit breakers, be sure to refer to UL Standard UL 508 A, Chapter SB4.2.3, Exception No. 1. For further questions regarding UL circuit breakers, please contact the appropriate certificate authority.
SB4.2.3 A high fault short-circuit current value for a motor controller, overload relay or combined motor controller as specified in SB4.2.2 (a) or (c) may be used as the short-circuit current value of the component if the specified branch circuit protection device is provided.
Exception 1: Where the specified BCPD is a Class CC, G, J, L, RK1, RK5 or T fuse with respect to the high fault SCCR, a fuse of a different class may be used at the same high fault rated power, provided the Ip let-through current and I2t of the new fuse are not greater than that of the specified fuse. See table SB4.2 for maximum let-through currents (Ip) and I2t.
Three-phase
Fuse protection
AX5160
AX5172
AX5190
AX5191
AX5192
AX5193
AC supply (max.)
80 A
100 A
125 A
150 A
200 A
225 A
24 V supply (max.)
4 AT
10 AT
Braking resistor
electronic
AX5160 and AX5172:
Can be used in supply networks with a maximum current-carrying capacity (SCCR) of 5 kA at 480 V. For mains-side fuse protection, use only UL-approved circuit breakers of class RK5 with a maximum rated current of 100 A.
AX5190, AX5191, AX5192, AX5193:
Can be used in supply networks with a maximum current-carrying capacity (SCCR) of 10 kA at 480 V. For mains-side fuse protection, use only UL-approved circuit breakers of class RK5 with a maximum rated current of 225 A.