Restrictions for Clock Frequency
Firmware ≥ v2.10 build 0015 allows setting different frequency values.
Restrictions for Clock Frequency 1:
Possible values of the clock frequency to be set: 2000, 2500, 3333, 5000 [kHz].
The clock frequency can be changed in the parameter P-0-0150 under:
Parameter channel → Data → BISS → Sensor mode: Max. clock speed
If other values are set, the software will use the next possible lower value. Lower clock frequency causes longer data transmission time.
Communication signals between AX5000 and encoder look like this:
Restrictions for Clock Frequency 2:
During the "Ack" period the encoder prepares for transferring the actual position value. With the rising edge at "Start" it signals to be ready and then starts transferring data.
Due to its internal cycles the AX5000 needs the position at certain point of time after it has started reading. This means the time from the first rising edge of the clock signal to the last CRC bit must not exceed 18µs.
Example:
Clock frequency: 3.333 MHz => Bit time = 1/ 3.333MHz = 0.3 µs
Number of bits to be transferred for a position telegram:
Example 1
Example 2
4 µs
8 µs
Preparing time of encoder ("Ack")
Number of bits
1
1
Start
1
1
CDS (Cyclic data slave, not used, always 0)
26
32
Position
1
1
Error (status)
1
1
Warning (status)
6
6
CRC
1
1
Stop/ Timeout
37
43
Number of clock cycles for complete telegram
Example 1
Example 2
Transmission time = 4 µs + 37 x 0.3 µs = 15.1 µs < 18 µs
Transmission time = 8 µs + 43 x 0.3 µs = 20.9 µs > 18 µs
    • The encoder in this example can be run at 3.333 MHz clock frequency.
    • For this case it is possible to set a value for "Pretrigger time encoder to sync" to start reading of the encoder earlier in the cycle:
20.9 µs - 18 µs = 2.9 µs
    • Set "Pretrigger time encoder to sync" = 4µs (1µs margin).
Restrictions for Clock Frequency 3:
Restrictions for Clock Frequency 4:
The value for the pretrigger must not exceed 15 µs!