Taking AX5206 as an example
The rated current for channel A is increased to 6.6 A and the peak current set to 11 A.
Reference values for the example calculation (channel A):
IDN | Description | Value |
S-0-0112 | Amplifier rated current | 12.0 A (fixed) |
P-0-0052 | Time limitation for peak current | 0 |
P-0-0090 | Channel peak current | 13.0 A (fixed) |
P-0-0091 | Channel rated current | 6.0 A (fixed) |
P-0-0092 (channel A) | Configured channel peak current | 11.0 A |
P-0-0093 (channel A) | Configured channel current | 6.6 A ( > P-0-0091, therefore select this value) |
tmax | Max. time for Ipeak | 7.0 s (fixed) |
Calculation for channel A
Total overcurrent time area of the device:
Maximum possible time (P-0-0052max):
The set maximum current of 11 A can be provided for 10.18 sec.
After that the current is limited to P-0-0093 (6.6 A).
The maximum settable time in P-0-0052 is thus 10.18 s.
Calculation for channel B
There is a limitation in P-0-0093 for channel B in this example:
P-0-0093max = S-0-0112 – P-0-0093 (Ch. A) = 5.4 A
Reference values for the example calculation (channel B):
P-0-0092 | Configured channel peak current | 11 A |
P-0-0093max | Configured channel current | 5.4 A |
The set maximum current of 11 A can be provided for 9.50 sec.
After that the current is limited to P-0-0093 (5.4 A).
The maximum settable time in P-0-0052 is thus 9.50 s.
![]() | Although a smaller value is set for P-0-0093, P-0-0093max is used in the calculation. |