FCD3, Over speed error.
The speed of the axis is higher than the parametrized maximum value in S-0-0113
Diagnostic Code (Hex.)
Diagnostic Code (Dez.)
FCD3
64723
Class
Type
Error
Runtime error
Standard Reaction
Reset
Closed loop ramp
Execute Reset-Command (S-0-0099).
Possible Causes
Solutions
The parametrized maximum value was exceeded.
Check whether the value of parameter S-0-0113 corresponds to the value from the technical data of the motor.
If the application requires a maximum value of 3000, you must set the value in S-0-0113 approx. 10% higher, so that the servo drive can adjust the 3000.
Analyze the value in S-0-0113.
An external force is acting on the drive system.
Analyze whether that is permissible and parameterize the drive system if necessary.
Analyze why the motor is turning so fast and rectify this.
Commutation error; the motor accelerates in an uncontrolled fashion.
Analyze why the commutation of the motor is not correct.
Further Information
AX5000_IDN-Description: "S-0-0113"