RK
ASCII - Command  | RK  |
Syntax Transmit  | RK [Data]  |
Syntax Receive  | RK <Data>  | Available in  |
Type  | Variable rw  | MMI  | Yes  | |
ASCII Format  | Integer16  | CANBus Object Number  | 35E6 (hex)  | |
DIM  | Counts  | PROFIBUS PNU  | 1830 (dec) IND = 0000xxxx (bin)  | |
Range  | 12000 ..19000  | DPR  | 230 (dec)  | |
Default  | 16384  |
Opmode  | All  | Data Type Bus/DPR  | Integer16  | |
Drive State  | -  | Weightning  |
Start Firmware  | 1.20  |
Configuration  | No  | Revision  | 1.3  | |
Function Group  | Feedback  | EEPROM  | Yes  | |
Short Description  | Gain Adjust for Resolver Sine Signal  | |||
The RK parameter can be used to correct any amplitude difference that may exist between the sine and cosine signals from the resolver. The relationships are as follows:
- RK = 16384 no alteration of the amplitude of the sine signal
 - RK < 16384 sine signal amplitude is reduced
 - RK > 16384 sine signal amplitude is increased
An incorrect setting of this correction factor will result in velocity/velocity variations (ripple) which are strongly dependent on the position.
The CALCRK command enables an automatic determination of the correction factor RK.
This value will not be changed by a parameter download, since it only depends on the equipment.