Fault correction
The following table describes a selection of faults. Depending on the application, other causes may be responsible for the fault. Conspicuous control behavior is the result of incorrect parameterization of the servo drive.
With multi-axis systems such as the AX8000, malfunctions may have different causes.
Error  | Cause  | ||||||||||||||||||
Motor standstill, no starting  | 1  | 2  |
  | 5  |
Electric cylinder runs sluggishly  | 1  |
  | 3  |
  | 5  | 6  |
  | 8  |
Start-up noises  |
  | 3  |
  | 5  | 6  |
  | 11  |
  | 19  |
Noises during operation  | 1  |
  | 3  |
  | 5  | 6  |
  | 8  |
  | 11  |
  | 19  |
High temperature at idling speed  |
  | 4  |
  | 7  |
  | 9  |
  | 19  |
High temperature under load  | 1  |
  | 3  |
  | 7  | 8  | 9  |
Untrue running behavior  |
  | 8  |
  | 10  | 11  |
  | 19  |
Grinding noises  |
  | 8  |
  | 12  |
  | 19  |
Brake fault  |
  | 13  | 14  |
Output stage fault  |
  | 5  |
  | 15  | 16  |
Feedback error  |
  | 17  | 18  |
Lack of braking effect  |
  | 5  | 6  |
Number  | Cause  | Solution  |
1  | Servo drive not enabled  | Set ENABLE signal and enable servo drive  |
Overload of the electric cylinder  | Check the load and if necessary reduce it, then restart and enable the servo drive. Set ENABLE signal  | |
Mechanical blockage of the electric cylinder  | Check mechanics and release blockage  | |
Holding brake [+] not released  | Check the control configuration of the holding brakes [+] and reconfigure if necessary  | |
2  | Phase interruption in the power supply or reversed motor phases  | Check servo drive and supply lines and replace any defective cables  |
3  | Phase interruption after power supply  | Check servo drive and supply lines and replace any defective cables  |
Power cable or feedback line with defective shield  | Check ground connection and shielding  | |
4  | Short-circuit in the voltage supply cable for the holding brake [+]  | Replace defective cable, measure and check cable after replacement  |
Output voltage of the servo drive too low  | Check the settings in the configuration and read out the electronic nameplate of the electric cylinder again  | |
Defective holding brake [+]  | Replace electric cylinder, then measure and check  | |
5  | Short circuit or earth leakage in the motor cable  | Replace defective motor cable, then measure and check  |
6  | Power connector not fitted correctly  | Check the connectors on the power connector and on the electric cylinder  |
Interruption in the feedback line or motor cable  | Check cables for wire break or crushing. Replace defective cables, then measure and check.  |
7  | Required force too high.  | Check design or configuration and adjust if necessary  |
The spindle drive is clamped in the application.  | Re-align electric cylinder or use compensating elements, see chapter Mechanical installation  | |
8  | Lubrication is not sufficient  | Check spindle for contamination and clean if necessary  |
Check maintenance interval and relubricate if necessary  | ||
Check length of working stroke and insert lubrication stroke if necessary  | ||
9  | Heat dissipation system of the electric cylinder not functioning  | Clean the surface of the electric cylinder and the servo drive as well as the heat sinks and exhaust air slots  |
Check the mounting depth of the servo drives and the electric cylinder.  | ||
10  | Shield of feedback line or motor cable defective or inadequate  | Check ground connection and shielding  |
11  | Servo drive gain is set too high.  | Reconfigure the parameters of the servo drive and adjust them if necessary  |
12  | Contamination or foreign bodies inside the electric cylinder  | Send in electric cylinder. The repair is carried out by the vendor.  |
Rotating parts chafing on the housing or electric cylinder components  | Inspect chafing parts and readjust if necessary  | |
Defective bearings; irreparable bearing damage  | Send in electric cylinder. The repair is carried out by the vendor.  |
13  | Short-circuit in the voltage supply cable for the holding brake [+]  | Replace defective cable, then measure and check  |
14  | Inadequate power supply of the holding brake [+]  | Check the settings in the configuration and read out the electronic nameplate of the electric cylinder again  |
15  | Short circuit or earth leakage in the electric cylinder  | Replace defective electric cylinder, then measure and check  |
16  | Insufficient power supply  | Check the settings in the configuration and read out the electronic nameplate of the electric cylinder again  |
17  | Interruption or crushing in the feedback line  | Check cables for wire break or crushing. Replace defective cables, then measure and check.  |
18  | Power connector of the electric cylinder incorrectly plugged in  | Check correct seating of the connector for feedback signals and correct if necessary  |
Loose fit of the feedback connector or no contact of the plug contacts with the power socket of the electric cylinder  | Check the connector assembly. Contact Beckhoff Service if necessary  | |
19  | Check spindle surface for damage and contamination  | Contact Beckhoff Service, avoid impacts on the spindle and sudden loads during operation and assembly  |