MC_LoadControl
MC_LoadControl 1:
This function block continuously exerts a torque, force or pressure of the specified value.
Positive torque, force and differential pressure is in the positive direction of velocity, pressure is physically unsigned. LoadUnit must match the unit of the value measured by the corresponding sensor.
Definition:
FUNCTION_BLOCK MC_LoadControl
    Axis               : Reference To AXIS_REF;
    Execute            : BOOL;
    Load               : LREAL;
    LoadRamp           : LREAL;
    LoadRampDerivative : LREAL;
    BufferMode         : EBufferMode;
    InLoad             : BOOL;
    Busy               : BOOL;
    Active             : BOOL;
    CommandAborted     : BOOL;
    Error              : BOOL;
    ErrorId            : UDINT;
MC_LoadControl 2: Inputs
Type
Default
Execute
Start the motion at rising edge.
Load
LREAL
#Invalid
Commanded load value ([LoadUnit]). It is approached using a defined ramp (LoadRamp).
LoadRamp
LREAL
#Invalid
Maximum load derivative ([LoadUnit/s], positive)
LoadRampDerivative
LREAL
#Ignore
Maximum load ramp derivative ([LoadUnit/s^2], positive). It can be left as 'Ignore' if no ramp derivative limit is desired.
BufferMode
EBufferMode
Aborting
Chronological sequence of the command
MC_LoadControl 3: In/Outputs
Type
Axis
Reference to the axis
MC_LoadControl 4: Outputs
Type
InLoad
Commanded load value reached
Busy
Function block is not finished and new output values are to be expected.
Active
Function block has active control on the axis.
CommandAborted
Command is aborted by another command.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
Versionsinformation
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5500 MC3 Base >= v4.0.6
