FD59, Error Power Management: Wrong external brake resistor found
The determined values of the external brake resistor connected do not correspond to the parametrized values in the TCDriveManager.
Diagnostic Code (Hex.) |
Diagnostic Code (Dez.) |
FD59 |
64857 |
Class |
Type |
Error |
Runtime error |
Standard Reaction |
Reset |
Closed loop ramp |
Execute Reset-Command (S-0-0099). |
Possible Causes |
Solutions |
General measurement error; measure the brake resistor and compare the ohmic value determined to the data on the type label. |
If the value corresponds, deactivate the internal test of the external brake resistor: To do this, set the IDN P-0-0204 "Disable DC link interface check" to "enable". Observe the application with regard to the proper operation of the external brake resistor. |
If the value does not correspond, exchange the brake resistor or enter the determined ohmic value in the TCDriveManager; afterwards, switch the 24 V supply off and on again. . |
![]() | Please consider this note! If you have ruled out the above measurement errors, you can switch off the brake resistor check via the IDN P-0-0204 "Bit 1". |