FD44, Mains supply: Phase error.
A phase of the 3-phase mains supply has failed.
Diagnostic Code (Hex.) |
Diagnostic Code (Dez.) |
FD44 |
64836 |
Class |
Type |
Error |
Runtime error |
Standard Reaction |
Reset |
Nc handling |
Execute Reset-Command (S-0-0099). |
Possible Causes |
Solutions |
The mains supply is faulty. |
Analyze the mains supply and rectify the fault. |
The 3-phase mains supply is continually afflicted by faults. |
By means of IDN P-0-0204, activate a filter that causes the phase monitoring to wait longer before triggering the error. |
You are operating the AX5000 on a single-phase mains supply. |
Deactivate the phase monitoring by means of IDN P-0-0204 bit 3. If you had assumed a 3-phase mains supply during the project engineering, check in the IDN P-0-0092 and P-0-0093 whether you need to enter a derating. |
![]() | Please consider this note! On no account should you deactivate the phase monitoring if a phase of the 3-phase mains supply has failed, as otherwise the AX5000 will be destroyed. |
Further Information |
AX5000_IDN-Description: "P-0-0092", "P-0-0093" and "P-0-0204" |