F2A1, Over-current error motor, measuring limit reached (X13 / X23).
The drive software detected an over-current on the motor phases. The limit of the current measuring range was reached.
Diagnostic Code (Hex.) |
Diagnostic Code (Dez.) |
F2A1 |
62113 |
Class |
Type |
Error |
Runtime error |
Standard Reaction |
Reset |
Shorted coils brake |
Execute Reset-Command (S-0-0099). |
Possible Causes |
Solutions |
This error depends on the total system configured: |
The solution depends on the total system configured: |
Asynchronous motor without feedback. |
Check the load conditions and if necessary activate the acceleration controller (IDNs P-0-0112, P-0-0113, P-0-0114 and P-0-0451) and/or the breakdown protection controller (IDNs P-0-0115, P-0-0116, P-0-0117 and P-0-0451). |
Synchronous motor, current-controlled with incremental feedback. |
Check the following IDNs: P-0-0165; S-0-0106; S-0-0107; S-0-0119; S-0-0120. |
Asynchronous motor with feedback. |
Check the parametrization of the current controller and the IDNs P-0-0107 and S-0-0106. |
Synchronous motor, current-controlled with absolute position information per pole pair. |
Check the parametrization of the current controller. |
Synchronous motor, current-controlled without feedback |
Further Information |
AX5000_IDN-Description: "S-0-0106; S-0-0107; S-0-0119; S-0-0120; P-0-0112; P-0-0113; P-0-0114; P-0-0115; P-0-0116; P-0-0117; P-0-0165; P-0-0451" |