Front side and operating elements
Front side and operating elements 1:
Front PS9771-2440-0000
Input terminals (screw terminals)
Designation (A)
Line input +
Line input -
N/C
Not connected
Front side and operating elements 2:
Earth input
Output terminals (screw terminals)
Designation (B)
2 identical positive poles, positive output
2 identical negative poles, negative output
Output voltage potentiometer
Designation (C)
Potentiometer cover
Multi turn potentiometer;
open the flap to adjust the output voltage.
Factory set: 24.1V at full output current, “Single Use” mode
DC-OK / Overload LED
Designation (D)
DC-OK LED (green)
• On:
the voltage on the output terminals is >90% of the adjusted output voltage.
Overload LED (red)
• On:
the voltage on the output terminals is <90% of the adjusted output voltage, or in case of a short circuit in the output.
• Flashing:
the shut-down has been activated or the unit has switched off due to over-temperature. I
Input voltage is required
“Parallel Use” / “Single Use” selector
Designation (E)
Jumper
Set jumper to “Parallel Use” when power supplies are connected in parallel to increase the output power.
In order to achieve a sharing of the load current between the individual power supplies, the “parallel use” regulates the output voltage in such a manner that the voltage at no load is approx. 4% higher than at nominal load.
See also chapter “Parallel use for redundancy”. A missing jumper is equal to a “Single Use” mode.
DC-OK relay / Shut down contact
Designation (F)
Push-in terminals
13 / 14
The DC-OK relay contact is synchronized with the DC-OK LED.
See chapter “DC-OK relay contact” for details.
Push-in terminals
15/ 16
Allows the power supply to be shut down. Can be activated with a switch contact or an external voltage.
See chapter “Shut-down input” for details.
LEDs
Indicators/LEDs
Overload LED
DC-OK LED
DC-OK contact
Normal mode
OFF
ON
Closed
During Extra Power
OFF
ON
Closed
Overload (Vout < 90%)
ON
OFF
Open
Output short circuit
ON
OFF
Open
Temperature Shut-down
flashing
OFF
Open
Active Shut-down input
flashing
OFF
Open
No input power
OFF
OFF
Open