Protective functions and safety features
Insulation resistance
> 500MOhm
In the delivery state between the mains power connection and signals, measured with 500 Vdc
> 500MOhm
In the delivery state between the mains power connection and the housing, measured with 500 Vdc
> 500MOhm
In the delivery state between the signal connections and the housing, measured with 500 Vdc
PE resistance
< 0.1 ohm
Resistance between the chassis ground terminal and the housing.
Protection class
N/A
Install the buffer module according to the rules of Class III
Protection class / ingress protection
IP 20
EN/IEC 60529
Overtemperature protection
Output overvoltage protection
Typ. 32Vdc
Max. 35Vdc
In the event of a defect in the internal buffer module, a redundant circuit limits the maximum output voltage. The buffering stops and automatically attempts to restart.
Internal input fuse
Overvoltage protection at the input
Max. 35Vdc
Device not damaged or defective
Reverse polarity protection at the input
Max. -35 Vdc
Touch current (leakage current)
The leakage current generated by the buffer module itself depends on the input voltage ripple and must be investigated in the final application. With an even DC input voltage, the leakage current generated is less than 100 μA.