Repeated pulse load
Typically a load current is not constant and varies with time. This power supply is designed to support loads with a higher short-term power demand (extra power). The short-term duration is hardware-controlled by an output power manager and is available repeatedly. If the extra power load lasts longer than the hardware controller allows, the output voltage drops. Extra power is available again after the extra power recovery time has elapsed (see Output chapter).
To avoid this, the following conditions must be met:
Repeated pulse load 1:
Repeated pulse loads, definitions; Max. duty cycle curve
Key
P0
Base load (W)
PPEAK
Pulse load (over 100%)
T0
Duration between pulses (s)
TPEAK
Pulse duration (s)
Calculation:
Duty cycle = TPEAK / (TPEAK + T0)
T0 = (TPEAK - (DutyCycle x TPEAK)) / DutyCycle
Example:
A load is operated continuously with 240 W (= 50% of the nominal output load).
From time to time a peak power of 720 W (= 150% of the nominal output load) is required for 1 second.
T0 = (TPEAK - (DutyCycle x TPEAK)) / DutyCycle = (1 s - (0.37 x 1 s)) / 0.37 = 1.7 s
Further examples of pulse load tolerance
PPEAK
P0
TPEAK
T0
720 W
480 W
1 s
>25 s
720 W
0 W
1 s
>1.3 s
600 W
240 W
1 s
> 0.75 s
720 W
240 W
0.1 s
>0.16 s
720 W
240 W
1 s
>1.6 s
720 W
240 W
3 s
>4.9 s