Overview
PS2001-4810-1001 | Power supply 48 V, 10 A, 1-phase, Extra Power, with EtherCAT interface
Overview 1:
  • AC 100-240 V wide-range input
  • Incl. EtherCAT interface
  • Width only 48 mm
  • Efficiency up to 96.2%
  • Excellent part-load efficiency
  • 120% peak power, 576 W
  • Precise triggering of fuses through high overload / peak current
  • Safe hiccup overload mode
  • Active Power Factor Correction (PFC)
  • Minimum inrush current surge
  • Full output between -25°C and +60°C
  • Current-sharing function for parallel use
The PS2001-4810-1001 is a 1-phase 48 V DC power supply with an integrated EtherCAT communication level suitable for applications with an output current of 10 A and an output power of 480 W. Thanks to the integration of EtherCAT technology, measurement data and internal device data can be processed directly by the controller. This makes it possible to influence the device directly via remote access. Device-internal parameter values, status bits and error messages can be read, configured and reset easily and conveniently via the TwinCAT automation software. In addition, the power supply provides extensive measured data for monitoring both the DC output range and the AC input range.
The power supplies with EtherCAT interface belong to the PS2000 family and have a width of just 48 mm. They have a wide-range input, Active Power Factor Correction (PFC) and inrush current limitation on the input side. The output operates according to the UI characteristic curve and switches to the safe hiccup mode in case of overload/short-circuit. The PS2001-xxxx-1001 features an Extra Power with a continuous maximum output power of 120% and is able to trigger fuses precisely with a short-term peak current. The status of the output voltage can be tracked via the process data and displayed via the DC-OK LED on the front of the housing.
Overview of technical data *)
PS2001-4810-1001
Output voltage
DC 48 V (nominal factory setting 48 V)
Adjustment range
48...56 V
Output current
Extra Power at ambient temperature below +45 °C
Nominal load at ambient temperature up to +60 °C
Derating at ambient temperature above +60 °C
AC 120 - 240 V, DC 150 - 300 V mains
12.0 A - 10.3 A (576 W)
10.0 - 8.6 A (480 W)
Linear derating 12.5 W/K
AC 100 V, DC 110 - 150 V mains
10.5 A - 9.0 A (504 W)
8.75 - 7.4 A (420 W)
Linear derating 10.5 W/K
Input voltage AC
AC 100...240 V -15% / +10%
Mains frequency
50...60 Hz ±6%
Input current AC
4.26 / 2.23 A at 120 / 230 Vac
AC input inrush current
10.0 /4.5 APeak at 120 / 230 Vac
Power factor
0.99 / 0.98 at 120 / 230 Vac
Input voltage DC
DC 110...300 V ±20%
Input current DC
4.64 / 1.66 A at 110 / 300 Vdc
Efficiency
94.8 / 96.2% at 120 / 230 Vac
Losses
26.6 / 18.9 W at 120 / 230 Vac
Hold-up time
32 / 32 ms at 120 / 230 Vac
Temperature range
-25°C...+70°C
Protocol / bus interface
EtherCAT / 2 x RJ45
Data transfer rate
100 Mbit/s
Dimensions (W x H x D)
48 mm x 124 mm x 127 mm (without DIN rail)
Weight
830 g
Approvals/markings
CE, cULus
*) All values are typical figures specified at 48 V, 10 A, 230 Vac, 50 Hz, +25°C ambient temperature and after a 5 minutes run-in time, unless otherwise noted