Safety features
Safety features
Protection class
I
Conforms to IEC 61140
PE (protective conductor) connection required
Insulation resistance
> 500MOhm
In the delivery state between input and output, measured with 500Vdc
> 500MOhm
In the delivery state between input and protective conductor, measured with 500Vdc
> 500MOhm
In the delivery state between output and protective conductor, measured with 500Vdc
> 500MOhm
In the delivery state between output and DC OK contacts, measured with 500Vdc
PE resistance
< 0.1Ohm
Resistance between the protective conductor connection and the housing near the DIN rail mounting bracket.
Leakage current
Typ. 0.12mA / 0.31mA
At 100Vac, 50Hz, TN, TT / IT network
Typ. 0.18mA / 0.45mA
At 120Vac, 60Hz, TN, TT / IT network
Typ. 0.30mA / 0.76mA
At 230Vac, 50Hz, TN, TT / IT network
Max. 0.16mA / 0.38mA
At 110Vac, 50Hz, TN, TT / IT network
Max. 0.23mA / 0.55mA
At 132Vac, 60Hz, TN, TT / IT network
Max. 0.39mA / 0.94mA
At 264Vac, 50Hz, TN, TT / IT network