Output circuit breakers
Standard circuit breakers (or UL1077 circuit breakers) are generally used for AC supply systems and can also be used for 24 V branches.
Circuit breakers are used to protect wires and circuits. If the ampere value and the characteristics of the circuit breaker are matched to the wire thickness used, the wiring is considered thermally safe, regardless of whether the circuit breaker opens or not.
To avoid voltage drops and situations with undervoltage in adjacent 24 V branches fed from the same source, a fast (magnetic) trip of the circuit breaker is desirable. Fast shutdown within 10 ms is required, which approximately corresponds to the hold-up time of PLCs. For this purpose, power supplies with high current reserves and large output capacitors are advantageous. Furthermore, the impedance of the faulty branch must be sufficiently small in order for the current to actually flow.
The following table contains typical test results that show which circuit breakers with B and C characteristics trip magnetically, depending on the wire cross-section and the wire length.
Maximal wire length*) for a fast (magnetic) tripping:
| 0.75 mm2 | 1.0 mm2 | 1.5 mm2 | 2.5 mm2 |
C-2A | 31 m | 37 m | 63 m | 98 m |
C-3A | 28 m | 34 m | 51 m | 78 m |
C-4A | 18 m | 25 m | 38 m | 58 m |
C-6A | 9 m | 11 m | 18 m | 26 m |
C-8A | 6 m | 7 m | 12 m | 14 m |
C-10A | 4 m | 6 m | 11 m | 13 m |
C-13A | 2 m | 2 m | 4 m | 7 m |
B-6A | 23 m | 28 m | 46 m | 66 m |
B-10A | 11 m | 14 m | 19 m | 32 m |
B-13A | 7 m | 11 m | 16 m | 29 m |
B-16A | 5 m | 6 m | 8 m | 15 m |
B-20A | 1 m | 1 m | 2 m | 4 m |
B-25A |
| 1 m |
*) Don't forget to double the distance to the load (or the cable length) when calculating the total cable length (plus and minus cable).
