Dielectric strength
The output voltage is earth-free and has no ohmic connection to earth.
The output is isolated from the input by double or reinforced insulation.
Type and component tests are carried out by the manufacturer. Field tests can be performed in the field using suitable test equipment that ramps up the voltage with a slow ramp (2s rising and 2s falling). Connect all input terminals and all output poles to each other before performing the tests. During the test, set the cut-off current to the value shown in the table below.
We recommend connecting either the positive pole, the negative pole or another part of the output circuit to the protective conductor system. This avoids situations in which the load starts unexpectedly or cannot be disconnected if an unnoticed earth leakage occurs.
Dielectric strength 1:
Dielectric strength
B*) When checking the input to DC-OK, make sure that the maximum voltage between DC-OK and the output is not exceeded (column D). When performing the test, we recommend connecting the DC OK contact pins and the output contact pins.
A
B
C
D
Type test
60s
2500Vac
3000Vac
1000Vac
500Vac
Component test
5s
2500Vac
2500Vac
500Vac
500Vac
Field test
5s
2000Vac
2000Vac
500Vac
500Vac
Setting the cut-off current
>10mA
> 10mA
> 20mA
> 1mA