Input inrush current
Active inrush current limitation (NTCs that are bridged by a relay contact) limits the inrush current after the input voltage is switched on.
The charge current of the interference suppression capacitors during the first few microseconds after switching on is not taken into account.
AC 100V
AC 120V
AC 230V
Max.
8Apeak
7Apeak
7Apeak
At +40°C, cold start
Typ.
5Apeak
4Apeak
4Apeak
At +25°C, cold start
Typ.
5Apeak
5Apeak
6Apeak
Switch-on energy
Max.
0.4A²s
0.5A²s
1A²s
Input inrush current 1:
Typical switch-on behavior at nominal load, 120Vac input voltage and 25°C ambient temperature
Input inrush current 2:
Typical switch-on behavior at nominal load, 230Vac input voltage and 25°C ambient temperature